Spray foam filled electrical outlets #189359 10/03/09 08:06 PM
Joined: Apr 2008
Posts: 20
N
nhsparky Offline OP
Member
I have a customer (recent widow) who lives in a large home on the lake. In the winter the wind pressure is so great she can't get her kitchen temp over 50. She recently had a spray foam contractor foam her attic. While there, she asked him if they could fill the electrical boxes. He said he could and he did! Three floors worth. When I found out and expressed my opposition and displeasure about it she got back in touch with them. They told her the foam is non flammable and code compliant.Although I intuitively know this is illegal, I cant find any code language to back me up. Any thoughts? My next call is to my state inspector, but I thought I would start here first.
Thanks,
Dave.

Work Gear for Electricians and the Trades
Re: Spray foam filled electrical outlets [Re: nhsparky] #189360 10/03/09 08:12 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
Is it listed for the application?

Last edited by sparkyinak; 10/03/09 08:13 PM.

"Live Awesome!" - Kevin Carosa
Re: Spray foam filled electrical outlets [Re: sparkyinak] #189362 10/03/09 08:24 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
Quote
110.12(B)Integrity of Electrical Equipment and Connections. Internal parts of electrical equipment, including busbars, wiring terminals, insulators, and other surfaces, shall not be damaged or contaminated by foreign materials such as paint, plaster, cleaners, abrasives, or corrosive residues. ...


I would include foam in that category


Greg Fretwell
Re: Spray foam filled electrical outlets [Re: sparkyinak] #189363 10/03/09 08:24 PM
Joined: Apr 2008
Posts: 20
N
nhsparky Offline OP
Member
Is it listed for the application?


I haven't seen any paper work yet. foam guy said he will bring it to her but I still can't believe filling an electrical box full of spray foam is acceptable.

Re: Spray foam filled electrical outlets [Re: nhsparky] #189367 10/03/09 10:39 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
If you fill the box with foam, what does that do to the device and wiring fill calculations? Won't the wiring devices be unable to get rid of their waste heat?
I'm sure that UL doesn't test these things wrapped up like a pig in a blanket.


Ghost307
Re: Spray foam filled electrical outlets [Re: ghost307] #189370 10/04/09 02:16 AM
Joined: Jul 2002
Posts: 8,379
Trumpy Offline
Member
I would get the MSDS from the installer and a statement in writing that this material is non-flammable.
If it is foam like I am imagining, it ISN'T non-flammable at all.
Having this sort of thing in such close proximity to a possible bad connection of what-not, is just asking for trouble.
There are better ways to achieve a good seal in boxes, you just need to use a bit of grey-matter.

You also have to ask about the quality of the house construction, if the building cannot be heated to any great degree.
I'd be talking to the Contractor about that, it is HIS problem.

Re: Spray foam filled electrical outlets [Re: Trumpy] #189371 10/04/09 02:26 AM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
I think it is a lot simpler than that. We regularly tag panels and boxes that get too much drywall mud in them on a 110.12(B) and require that they get cleaned out.
(don't we?).
That is clearly not a flammability issue it is "contamination" by a "foreign material".
We can think of a number of reasons why the foam is bad but I wouldn't over think this.


Greg Fretwell
Re: Spray foam filled electrical outlets [Re: gfretwell] #189373 10/04/09 03:34 AM
Joined: Jul 2002
Posts: 8,379
Trumpy Offline
Member
Originally Posted by gfretwell
We regularly tag panels and boxes that get too much drywall mud in them on a 110.12(B) and require that they get cleaned out.

Who in their right mind would leave a panel open to plaster and paint damage, in a new install?
There are things called masking tape and paper (or plastic film).
There is no reason that these materials should be finding their way into electrical enclosures, no matter how small.

Re: Spray foam filled electrical outlets [Re: Trumpy] #189374 10/04/09 11:24 AM
Joined: Sep 2002
Posts: 908
N
NORCAL Offline
Member
Originally Posted by Trumpy
Originally Posted by gfretwell
We regularly tag panels and boxes that get too much drywall mud in them on a 110.12(B) and require that they get cleaned out.

Who in their right mind would leave a panel open to plaster and paint damage, in a new install?
There are things called masking tape and paper (or plastic film).
There is no reason that these materials should be finding their way into electrical enclosures, no matter how small.


Cardboard being removed by others, stupid painters who are too lazy to mask it off, the list goes on and on.....

Re: Spray foam filled electrical outlets [Re: NORCAL] #189379 10/04/09 03:24 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Romex foamed in this manner must loose its ability to dump heat.

This is an issue worthy of an NEC revision/ NTL evaluation.

And as for the box foam-fill...

Of course it's a violation. The urethane foam is combustible.


Tesla
Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,604 Are you busy
209,528 Re: Forum
196,892 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3