I was looking at a job that had a 225KVA transformer suspended from the ceiling in a large utility room of Building. Below the transformer there are 2 - 400amp disconnects. The secondary conductors go to these two switches. Is this allowed, or do you need one single disconnect? I believe the transformer is 3 phase 480V to 208V. There is a breaker on the Primary side also. Is there a section in the code about the number of disconnects allowed on the secondary side?
Thanks

Horizontal Ad
Joined: Mar 2003
Posts: 849
Y
Member
240.21 (C) Each set of conductors feeding seperate loads Shall be permitted to connected to a transformer secondary. (Notice EACH)Devices must be grouped to meet 450.3 (B) note 2
NEC 2005 Handbook Details this clearly on page 170.
Yoopersup

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
The transformer is protected under article 450.3. If the primary disconnect is sized at not more than 125% of the primary FLA, a single disconnect is not required on the secondary.

The secondary conductors are protected by the tap rules in 240.21(C). There are situations where a set of tap conductors can feed multiple devices.

Last edited by JBD; 09/22/09 10:29 PM.
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
I checked that 240.21 (C) and you were right on with that. We may leave the 2 Disconnects alone and change a distribution panel downstream from those.
Stay Safe



Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
The Watt Doctor
The Watt Doctor
Humble, TX
Posts: 440
Joined: December 2001
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
327,590 Are you busy
252,478 Re: Forum
235,122 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5