#189171 09/22/09 09:06 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
I was looking at a job that had a 225KVA transformer suspended from the ceiling in a large utility room of Building. Below the transformer there are 2 - 400amp disconnects. The secondary conductors go to these two switches. Is this allowed, or do you need one single disconnect? I believe the transformer is 3 phase 480V to 208V. There is a breaker on the Primary side also. Is there a section in the code about the number of disconnects allowed on the secondary side?
Thanks

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Mar 2003
Posts: 849
Y
Member
240.21 (C) Each set of conductors feeding seperate loads Shall be permitted to connected to a transformer secondary. (Notice EACH)Devices must be grouped to meet 450.3 (B) note 2
NEC 2005 Handbook Details this clearly on page 170.
Yoopersup

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
The transformer is protected under article 450.3. If the primary disconnect is sized at not more than 125% of the primary FLA, a single disconnect is not required on the secondary.

The secondary conductors are protected by the tap rules in 240.21(C). There are situations where a set of tap conductors can feed multiple devices.

Last edited by JBD; 09/22/09 09:29 PM.
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
I checked that 240.21 (C) and you were right on with that. We may leave the 2 Disconnects alone and change a distribution panel downstream from those.
Stay Safe



Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,722
Joined: October 2000
Top Posters(30 Days)
Trumpy 9
NORCAL 5
Popular Topics(Views)
300,382 Are you busy
230,030 Re: Forum
214,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5