split bonding bushing or similar device? #189029 09/16/09 12:30 PM
Joined: Dec 2001
Posts: 300
M
maintenanceguy Offline OP
Member
I've got a lot of electrical panels with conduit entering through holes that have been drilled across concentric knockouts. We'd like to add bonding bushings to these but would rather not have to "unwire" the whole panel to feed the conductors through the bushings.

I know I've seen bonding clamps or clips that slip under the locknut where the fitting enters the panel. I don't know what to call them and can't find them now. Maybe they were never legal, I can't even remember where I've seen them. But I'd like to find an easier way to add bonding.

Hoping somebody has a great idea.

Work Gear for Electricians and the Trades
Re: split bonding bushing or similar device? [Re: maintenanceguy] #189030 09/16/09 01:32 PM
Joined: Jul 2004
Posts: 9,541
G
gfretwell Offline
Member


Greg Fretwell
Re: split bonding bushing or similar device? [Re: gfretwell] #189031 09/16/09 02:55 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
Does that slip under a bushing?
It looks like the opening is not large enough to slide in from the side; but would have to be treaded over the end of the conduit.


Ghost307
Re: split bonding bushing or similar device? [Re: gfretwell] #189035 09/16/09 03:43 PM
Joined: Dec 2001
Posts: 300
M
maintenanceguy Offline OP
Member
exactly what I was looking for. Will require removing any bushings/locknuts from the fitting but I won't have to pull all the wires through the wedge.

Just called the electrical supplier and they said "A what?" but found it with the T&B number on the pdf you included.

Thanks.

Re: split bonding bushing or similar device? [Re: maintenanceguy] #189093 09/18/09 08:02 PM
Joined: Jul 2002
Posts: 680
W
walrus Offline
Member
From my experience, if you have a plastic bushing you'll have to drill a hole in it to get the bonding screw into the thread of the conduit

Re: split bonding bushing or similar device? [Re: walrus] #189095 09/18/09 08:39 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member


The pdf file Greg posted from T&B shows a "T&B Series 122 Metallic Bushing" below the wedge.

I wonder if this is part of the bonding wedge's listing.

rolleyes


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,948 Are you busy
205,833 Re: Forum
193,912 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3