Joined: Dec 2001
Posts: 300
M
Member
I've got a lot of electrical panels with conduit entering through holes that have been drilled across concentric knockouts. We'd like to add bonding bushings to these but would rather not have to "unwire" the whole panel to feed the conductors through the bushings.

I know I've seen bonding clamps or clips that slip under the locknut where the fitting enters the panel. I don't know what to call them and can't find them now. Maybe they were never legal, I can't even remember where I've seen them. But I'd like to find an easier way to add bonding.

Hoping somebody has a great idea.

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member


Greg Fretwell
Joined: May 2005
Posts: 984
Likes: 1
G
Member
Does that slip under a bushing?
It looks like the opening is not large enough to slide in from the side; but would have to be treaded over the end of the conduit.


Ghost307
Joined: Dec 2001
Posts: 300
M
Member
exactly what I was looking for. Will require removing any bushings/locknuts from the fitting but I won't have to pull all the wires through the wedge.

Just called the electrical supplier and they said "A what?" but found it with the T&B number on the pdf you included.

Thanks.

Joined: Jul 2002
Posts: 680
W
Member
From my experience, if you have a plastic bushing you'll have to drill a hole in it to get the bonding screw into the thread of the conduit

Joined: Dec 2000
Posts: 4,291
Member


The pdf file Greg posted from T&B shows a "T&B Series 122 Metallic Bushing" below the wedge.

I wonder if this is part of the bonding wedge's listing.

rolleyes


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Top Posters(30 Days)
triple 3
BigB 3
Popular Topics(Views)
303,204 Are you busy
232,198 Re: Forum
216,942 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5