split bonding bushing or similar device? #189029
09/16/09 01:30 PM
09/16/09 01:30 PM
M
maintenanceguy  Offline OP
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
I've got a lot of electrical panels with conduit entering through holes that have been drilled across concentric knockouts. We'd like to add bonding bushings to these but would rather not have to "unwire" the whole panel to feed the conductors through the bushings.

I know I've seen bonding clamps or clips that slip under the locknut where the fitting enters the panel. I don't know what to call them and can't find them now. Maybe they were never legal, I can't even remember where I've seen them. But I'd like to find an easier way to add bonding.

Hoping somebody has a great idea.

Work Gear for Electricians and the Trades
Re: split bonding bushing or similar device? [Re: maintenanceguy] #189030
09/16/09 02:32 PM
09/16/09 02:32 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,228
Estero,Fl,usa


Greg Fretwell
Re: split bonding bushing or similar device? [Re: gfretwell] #189031
09/16/09 03:55 PM
09/16/09 03:55 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 943
Chicago Illinois USA
Does that slip under a bushing?
It looks like the opening is not large enough to slide in from the side; but would have to be treaded over the end of the conduit.


Ghost307
Re: split bonding bushing or similar device? [Re: gfretwell] #189035
09/16/09 04:43 PM
09/16/09 04:43 PM
M
maintenanceguy  Offline OP
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
exactly what I was looking for. Will require removing any bushings/locknuts from the fitting but I won't have to pull all the wires through the wedge.

Just called the electrical supplier and they said "A what?" but found it with the T&B number on the pdf you included.

Thanks.

Re: split bonding bushing or similar device? [Re: maintenanceguy] #189093
09/18/09 09:02 PM
09/18/09 09:02 PM
W
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
From my experience, if you have a plastic bushing you'll have to drill a hole in it to get the bonding screw into the thread of the conduit

Re: split bonding bushing or similar device? [Re: walrus] #189095
09/18/09 09:39 PM
09/18/09 09:39 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,268
Fullerton, CA USA


The pdf file Greg posted from T&B shows a "T&B Series 122 Metallic Bushing" below the wedge.

I wonder if this is part of the bonding wedge's listing.

rolleyes


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
twh 5
Popular Topics(Views)
247,675 Are you busy
184,993 Re: Forum
174,297 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.005s) Memory: 0.9774 MB (Peak: 1.1252 MB) Zlib enabled. Server Time: 2018-06-23 08:04:53 UTC