ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Video door bell causing chime activation of coil
by gfretwell. 12/10/18 12:35 AM
Conduit fill Calculations
by gfretwell. 12/08/18 08:39 PM
Pull out fuse panel?
by Trumpy. 12/06/18 02:12 AM
Swimming Pool question
by HotLine1. 12/05/18 12:37 PM
Tingle off the water spigot
by rmiell. 11/30/18 01:03 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 27 guests, and 25 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
brain teaser #188858
09/07/09 07:37 PM
09/07/09 07:37 PM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I have a AFI that keeps tripping when I turn the lights on, when I take all the bulbs out the circuit holds...ok bad AFI right? Wrong, for kicks and giggles I removed the neutral from the AFI and landed in the busbar and tested the lights again, and again they tripped the breaker. Anybody seen this b-4? It seems if the switch leg was crissed cross to the neut, then the circuit would trip regardless if the lamp was present. What are some other reasons you guys can think of?

2017 / 2014 NEC & Related Books and Study Guides
Re: brain teaser [Re: watersparkfalls] #188859
09/07/09 07:50 PM
09/07/09 07:50 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Neutrals from two circuits tied together or a neutral faulted to ground. Arc fault breakers also trip on a ground fault.

Re: brain teaser [Re: twh] #188867
09/08/09 12:55 AM
09/08/09 12:55 AM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I agree with you twh. But I took the neut out of series with the AFI(standard breaker now. I should be more specific that with the light bulbs out, I can turn switch on and read 120V on the switch leg side of the switch. Put in lamp and turn same switch and breaker trips.

Re: brain teaser [Re: watersparkfalls] #188870
09/08/09 02:14 AM
09/08/09 02:14 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,253
SI,New Zealand
Have you tried a different lamp in the fitting, the filament may be about to break.

Re: brain teaser [Re: Trumpy] #188876
09/08/09 10:20 AM
09/08/09 10:20 AM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
Shared Neutral downstream? AFCIs do not like shared neutrals, anywhere in the circuit. The fact that the AFCI trips when the lights go on, but not before, may further indicate the shared neutral possibility. Directly landing the neutral in the panel would have no affect on this issue. The neutral would still be shared within the branch circuit(s).

Good Luck!

Re: brain teaser [Re: Zapped] #188952
09/12/09 10:27 PM
09/12/09 10:27 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Iíve seen that exact same thing happen twice before. Both were because of damaged NM cables in the walls on new construction. The neutral and grounding conductor where mashed together in the wall. Luckily these were not on my own jobs, but I still had the unfortunate task of locating the problems for someone else.

Sometimes the grounding conductor and neutral are touching somewhere downstream in one of the receptacle outlets. It could cause AFCI tripping when a load is applied, meaning something is plugged in or a light on the circuit is turned on.

Re: brain teaser [Re: twh] #189526
10/14/09 12:38 PM
10/14/09 12:38 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Originally Posted by twh
Neutrals from two circuits tied together or a neutral faulted to ground. Arc fault breakers also trip on a ground fault.
Removing the neutral from the AFI and landing it directly to the bus bar will trip out the unit on ground fault if any current at all passes through the hot conductor, just like if you'd done it to a GFCI. This method can't be used to troubleshoot.

If the AFCI only trips when the light switch is turned on, even if there are no bulbs in it, I suspect a wiring fault with the hot conductor, either a crossed neutral connection or a short circuit somewhere. Nail through NM will do this. At least you can narrow it down to that lighting string!

Either way, it's been a month, did you ever find the cause?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,171 Are you busy
189,160 Re: Forum
178,836 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 15 (0.004s) Memory: 0.9864 MB (Peak: 1.1437 MB) Zlib enabled. Server Time: 2018-12-12 21:06:51 UTC