ckt size #188573
08/18/09 01:02 PM
08/18/09 01:02 PM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I have a septic motor running amps 12 and a LRA of 40.
Septic guy has botched this septic up (don't get me started) Now he has a 240 volt motor(this one mentioned) I have it wired 120volt now and can change it to 240 easy enough without having to open up tank lid(float controls- power in to one float-which feeds through second float and spliced to motor-neutral tied to motor)so you see easy to convert 120 at panel to 240 and run separate power for low voltage alarm.
My question is "at 12 amps would 20 amp circuit be enough to feed motor and start up current"?

2017 / 2014 NEC & Related Books and Study Guides
Re: ckt size [Re: watersparkfalls] #188574
08/18/09 01:43 PM
08/18/09 01:43 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,252
Estero,Fl,usa
I bet it will be fine.


Greg Fretwell
Re: ckt size [Re: gfretwell] #188585
08/19/09 09:41 AM
08/19/09 09:41 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,349
not that it's relevant to your Q watersparkfalls , but i'm reading a particular design issue that's a pet peeve of mine here

i like all the leads for the motor, float controls, and or alarm(s) to be passed through a conduit uncut to a JB, and then that conduit sealed

imho, i have not yet seen a 'septic proof' JB that can be utilized and survive a methane atmosphere for any length of time

also, a disco placed as close as possible is also a consideration

and.....i'm really really tired of holding my breath trying to get meter readings on a failed system

~S~

Re: ckt size [Re: sparky] #188590
08/19/09 02:34 PM
08/19/09 02:34 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,252
Estero,Fl,usa
I never did a septic pump but when we did lift pumps I wanted seal offs on the conduits coming out of the pit if they couldn't demonstrate that they turned the air over to reduce the concentration of methane.


Greg Fretwell
Re: ckt size [Re: gfretwell] #188591
08/19/09 03:13 PM
08/19/09 03:13 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I do not advise that any attempts be made to 'seal' the conduit. I do like the idea of a junction box NEXT to the sump, though.

Indeed, I favor a grossly oversized conduit, and might even like it if there were separate conduits for the pump and float cables.

Let's look at this a bit closer. First, what is a 'junction box?? I most certainly do NOT mean any sort of metal box with a gasket. Rather, I am referring to the fiberglass or concrete 'handholes' that have open bottoms. These are set atop a layer of gravel, and (ideally) have the conduits use a sweep to enter them vertically, from the bottom.

Will an overfilled sump also fill the box? Yes. Rain and ground water will also enter. The open bottom means that they will also drain.

The reason for large conduit is that, over time, the cable insulation swells considerably. This can make it impossible to replace the entire length of cable.

Splices in the box are made using some sort of waterproof method; I prefer simple wire nuts, dipped in Scotch-Kote, and left pointing 'up.'

If you have to splice in the pit, do it leaving enough cable that the next time you can do it from ABOVE the pit. I like the Ideal UF splice kit for power leads; it has a 4-port set screw arrangement that allows for ready replacement the next time, or for easy rotation reversal of three phase pumps.

If you have to replace an existing junction box in a pit, use a PVC one. The 'home centers' carry very affordable ones by Carlon; I think a 12x12x4 cost me about $25. These are nice NEMA-4 boxes with proper gaskets. I use Scotch-kote to secure the gasket to the cover. Where cables enter, I use the fittings that have rubber grommets in them.

Re: ckt size [Re: renosteinke] #188597
08/19/09 10:58 PM
08/19/09 10:58 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,349
well we're forgetting the disco within sight here, aren't we?

best possible scenario, all wires come up to a loto switch on a post by the sewer entrance, there's usually enough SO cord

funny how the manufacturer's instructions always say 'to be installed by a licensed electrican' , yet mention nothing of it, and show pictorals of their own 'sewer proof' boxes without one eh?

the first consession is the nothing visible one, where a greenlee ground box may be used to displace the splicing from the methane (and from the worker being exposed to it, for you osha compliant sorts)

the last thing i'd do is a pvc box in the sewer hole. I tell people it won't last, and it usually doesn't.

last one i did , the lady insisted on not seeing anything in her pristine back yard, so it was the pvc box, the so cord connectors, as well as the small split bolt conn coated with scotchcote, sealed with duc seal, taped with splice tape within it aka= bomb proof

the lady had the access hole covered with 6" of dirt & grass...

it failed within a years time.........

take it from a dude who's crawled in enough sh*tholes

don't make a splice of any sort in them, unless your really really tolerant.....

~S~




Re: ckt size [Re: sparky] #188606
08/20/09 02:10 AM
08/20/09 02:10 AM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I am not sure we are talking about the same septic design.
The type I am referring to is a 3 tank system(because its on a lake[two is more typical}) The first tank is solids, when the water level reaches spill over then that black water goes into tank #2 which spills over into third tank via a filter that I think makes this gray water(this I am not sure of though) any way inside this tank sits said 12 Amp motor which pumps it 500+ feet to drain field tank which has two tanks up there.
Anyway inside #3 tank is a plastic JB which power, float and motor splice using the blue wet location wire nuts. The low voltage high alarm is run through LB. In both cases using direct burial wire outside tank back to house, where disco is mounted. I changed breaker to 2 pole 20Amp and it is working fine. Thanks for all the posts, interesting.
H2O

Re: ckt size [Re: watersparkfalls] #188610
08/20/09 06:54 AM
08/20/09 06:54 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,349
I've actually done that same setup myself watersparkfalls

for the most part, the diggers here install a pipe directly into the older style one tank systems

i've gone toe to toe with many of them, posing that i don't dig, you don't wire....

they mainly view me as a professional snot, which i make no bones about

i'm older, uglier, and if anyone wants a trouble free system i want it done my way

~S~




Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,623 Are you busy
186,362 Re: Forum
175,828 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 15 (0.004s) Memory: 0.9972 MB (Peak: 1.1575 MB) Zlib enabled. Server Time: 2018-08-19 09:43:19 UTC