Sign Disconnect #188420
08/07/09 07:58 PM
08/07/09 07:58 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Article 600.6 ask for a disconnect for a sign. If a sign builder installs a switch as an integral part of the sigh does this satisfy the requirement? One must realize that the UL standard does not require a disconnect as part of the requirements for sign construction.


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Sign Disconnect [Re: George Little] #188422
08/07/09 09:25 PM
08/07/09 09:25 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,253
Estero,Fl,usa
If it was at the circuit entry into the sign, disconnected all ungrounded conductors and was marked as the disconnect with an "off" position I would allow it.


Greg Fretwell
Re: Sign Disconnect [Re: gfretwell] #188451
08/09/09 07:29 PM
08/09/09 07:29 PM
L
luckyshadow  Offline
Member
Joined: Jan 2005
Posts: 315
Maryland USA
yes a factory installed disconnecting switch that disconnects all ungrounded conductors is allowed

Re: Sign Disconnect [Re: luckyshadow] #188489
08/11/09 04:57 PM
08/11/09 04:57 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I guess I left out a very key point. The branch circuit enters the back of the sign enclosure, travels through the sign and then exits the sign to terminate on the line side of a WP switch mounted on the sign. The load side of the switch has conductors that re-enter the sign enclosure and connect up to the Xformer of the sign. I feel that this a violation of 600.6 since the switch does not disconnect all un-grounded conductors in the sign. What do you think?


George Little
Re: Sign Disconnect [Re: George Little] #188494
08/11/09 07:36 PM
08/11/09 07:36 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,253
Estero,Fl,usa
Note I said "at the circuit entry into the sign". I agree with you, either move the disconnect to the conduit entry point or change where the conduit enters to make it next to the switch, preferably in a separate enclosure within the sign.
This could be as simple as a 4x4 deep ring that covered the switch terminals and conduit entry with a blank cover on the other side.
I believe the purpose of the disconnect is to make the interior of the equipment safe. I am not making a proposal but I do think a label over the disconnect enclosure saying something like "line voltage present with disconnect off" is a good idea.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,629 Are you busy
186,369 Re: Forum
175,846 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.004s) Memory: 0.9686 MB (Peak: 1.1091 MB) Zlib enabled. Server Time: 2018-08-19 21:50:08 UTC