1,816
12
I got in rather heated conversations with ambulance manufactures, one in Ark and one here in Houston. They would install a small panel in the unit served by a shore power cord. They would hook the neutrals and grounds on the same buss. The panel would serve several chargers and on later units, onboard AC unit. The first complaint I got was when the EMT (Firefighter) unplugged the cord he would get a shock. When the cord was pulled, the neutral would break first making the chassis hot for a second. I isolated the neutral and solved the problem. Told the manufactures and they both said the NEC does not apply to them and that the way they wired the panels was correct. I sent a certified letter to both, telling them they would be libel if someone got killed. Some smaller fire dept. have substandard wiring. If you were to plug the unit into a ungrounded ckt with reverse polarity, the whole chassis would be hot. Speaking of campers, lots of campers were wired like this with the neutrals and grounds bonded together. They trip a GFCI real quick. Most have a 30a cord that is connected to a non GFCI ckt at the camp site. Trouble comes when someone uses a 30a to 15a adapter in a GFCI outlet. I agree camper supply co have some not so great adapters, a cord to plug a 30a in a 50a plug and such. In your case, I have less of a problem plugging a 30a-50a plug in a 15,20,or 30 ckt even if the single ckt supplies both poles than a 40-50a ckt suppling a 30a or less load. As long as the wire size matches the source breaker size. Robert
Posts: 8,450 Likes: 4
Over here in the sticks, You are not allowed to have a cord or anything protrude from a caravan/trailer.
It must be connected to the trailer with an "appliance inlet" that has male pins and is permanently installed on the side of the "vehicle". You connect your live source with a female (weather-proof) cord connector, RCD/GFCI protection comes from the source of supply.
For those that have heard of it, the connectors must be rated to IP 56 (dust/moisture proofing).
One thing I would stipulate though, with regard to the flexible cords, is get the heaviest insulation possible, for the size of wires, these cords will get knocked around, run over and generally abused. I'm involved with Civil Defence over here and our gear gets a really hard time.
Robert,
I can understand the ambulance manufacturers asserting that the NEC doesn't apply to them, but connecting the neutral and ground together strikes me as both pointless and dangerous. I can only imagine how thrilled the operator would be the first time he plugged it into an outlet with reversed hot and neutral. Ka-boom.
Mike,
The currently-installed cords are only a few feet long, and they tuck into a storage space so they don't protrude for travel. Nevertheless, I hate them, and they're going to be replaced with a recessed inlet as you described. I rather like the marine-grade ones with the locking ring on the cord cap, which I believe are IP65.
Regards, John