gas pipe used as grounding electrode #188087
07/21/09 10:38 AM
07/21/09 10:38 AM
C
Chris Rudolph  Offline OP
Member
Joined: May 2001
Posts: 160
Winter Park,Fl USA
I have updated the service,150 amps,breaker panel,and installed a new grounding system in a single family house with basement in Upstate New York.The inspector said all was done well except that I had to clamp the grounding electrode conductor to the gas pipe in the basement.
Is this a violation of NEC 2002 250.52 B 1?
Chris

2017 / 2014 NEC & Related Books and Study Guides
Re: gas pipe used as grounding electrode [Re: Chris Rudolph] #188089
07/21/09 11:28 AM
07/21/09 11:28 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
That is not the ground electrode, it is bonding the gas pipe (250.104(B))
He also could have said you bond to the circuit EGC "likely to energize" the pipe. That will usually be the largest piece of electrical equipment connected to the gas pipe. (range electric igniter, furnace blower etc)
He might even say that was the A/C compressor via the freon line set to the A coil in the furnace. The safest alternative is the GEC, then all bases are covered.


Greg Fretwell
Re: gas pipe used as grounding electrode [Re: gfretwell] #188103
07/21/09 03:14 PM
07/21/09 03:14 PM
C
Chris Rudolph  Offline OP
Member
Joined: May 2001
Posts: 160
Winter Park,Fl USA
That sounds good to me because I had the GEC attached to the water pipe and a 8 ft ground rod that I had driven

Chris

Re: gas pipe used as grounding electrode [Re: Chris Rudolph] #188124
07/22/09 01:23 PM
07/22/09 01:23 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Chris
One reason to bond the pipe is in case it gets hit by lightning and brings the energy into the house. Here the gas pipes in the ground are plastic but some places are metal. The gas meters usually have a dielectric fitting to isolate the interior piping from the exterior. We always want the bonding connection on the house side of the meter and the gas company wants it there too. the dielectric fitting is to control galvanic corrosion on the underground gas pipes.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,230 Are you busy
189,198 Re: Forum
178,881 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.005s) Memory: 0.9606 MB (Peak: 1.0942 MB) Zlib enabled. Server Time: 2018-12-16 06:19:03 UTC