We've all had it happen. We're quite happily making just the right hole in just the right place, when one of those pre-punched KO's breaks free. We're left with a big hole to fix.
It often looks something like this:
There are a number of reasons we don't want to leave that hole open. If nothing else, we don't want a colony of wasps to set up housekeeping in the panel.
I was surprised to learn that the parts house actually had reducing washers for 2-1/2" pipe. I was also pleased when I was able to trim the washers with my aviation snips. Here's the result:
Now, this is not the first time I've had to deal with this issue. I was hoping for a better solution - or, perhaps, some trick to prevent it from happening in the first place.
The longer I'm in the trade, the less I like those pre-punched KO's!
Reno, Prepunched k.o.'s probably cost more labor time over the years than any other annoying thing. Most electricians would agree with you that they offer little benefit especially when using strut to support conduits.
The handiest method to blank off k.o.'s I have found is to use a 4" square blank or other piece of code gage metal bolted over the knockout. Good idea on the reducing washer too!