hey, does a shed need to be put on a GFCI breaker, or just the outlets lead by a GFCI outlet?? thanks
-Joe “then we'll glue em' then screw em'” -Tom Silva TOH
|
|
|
|
|
Joined: Aug 2001
Posts: 335
Member
|
Assuming there is a panel in it, the feeder does not. That being said ... In my area the AHJ determination was that it is treated like an unfinished basement. His logic was that since the receps in the shed will have grade level access for yard tools (used ouside) treat them as if they were outside. If you're only taking one circuit to it and the plan is to feed it GFCI protected (from the house), either a GFCI breaker or GFCI recep will do the trick. (recep is a lot cheaper)
|
|
|
|
|
Joined: Sep 2002
Posts: 947 Likes: 4
Member
|
See 210.8 2005 /2008 NEC (A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel. (1) Bathrooms (2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use (3) Outdoors Exception to (3): Receptacles that are not readily accessible and are supplied by a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed in accordance with 426.28. (4) Crawl spaces — at or below grade level (5) Unfinished basements — for purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like Exception to (5): A receptacle supplying only a permanently installed fire alarm or burglar alarm system shall not be required to have ground-fault circuit-interrupter protection. FPN: See 760.41(B) and 760.121(B) for power supply requirements for fire alarm systems. Receptacles installed under the exception to 210.8(A)(5) shall not be considered as meeting the requirements of 210.52(G). (6) Kitchens — where the receptacles are installed to serve the countertop surfaces (7) Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink (8) Boathouses
That was a copy & paste from the 2008 NEC.
|
|
|
|
|
Joined: Mar 2008
Posts: 144
OP
Member
|
Assuming there is a panel in it, the feeder does not. That being said ... In my area the AHJ determination was that it is treated like an unfinished basement. His logic was that since the receps in the shed will have grade level access for yard tools (used ouside) treat them as if they were outside. If you're only taking one circuit to it and the plan is to feed it GFCI protected (from the house), either a GFCI breaker or GFCI recep will do the trick. (recep is a lot cheaper) There is no Panel/Sub-panel in the shed, just a single 12/2 with ground going out to the shed as a feed.
-Joe “then we'll glue em' then screw em'” -Tom Silva TOH
|
|
|
|
|
Joined: Mar 2008
Posts: 144
OP
Member
|
See 210.8 2005 /2008 NEC (A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel. (1) Bathrooms (2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use (3) Outdoors Exception to (3): Receptacles that are not readily accessible and are supplied by a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed in accordance with 426.28. (4) Crawl spaces — at or below grade level (5) Unfinished basements — for purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like Exception to (5): A receptacle supplying only a permanently installed fire alarm or burglar alarm system shall not be required to have ground-fault circuit-interrupter protection. FPN: See 760.41(B) and 760.121(B) for power supply requirements for fire alarm systems. Receptacles installed under the exception to 210.8(A)(5) shall not be considered as meeting the requirements of 210.52(G). (6) Kitchens — where the receptacles are installed to serve the countertop surfaces (7) Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink (8) Boathouses
That was a copy & paste from the 2008 NEC. Thanks, what i am going to do is on the feed in, i will add an inline GFI switch (the kind with only the buttons, no outlets)(like this: http://www.alibaba.com/product-free/104072404/2006_UL_listed_GFCI_ground_fault/showimage.html )
-Joe “then we'll glue em' then screw em'” -Tom Silva TOH
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
Joe:
As Norcal posted above.... "(2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use"
John
|
|
|
|
|
Joined: Mar 2008
Posts: 144
OP
Member
|
Joe:
As Norcal posted above.... "(2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use"
i see, and i have to use the GFI recep, as i said above, because the panel in the garage is a screw in fuse panel, hopefully going to get upgraded too
-Joe “then we'll glue em' then screw em'” -Tom Silva TOH
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
Interesting link... Pic is a faceless (deadfront) GFI; text reads 'receptacle. Side pics are GFI receptacles. $3.xx(US) ea, 3000 pc minimum. Interesting?
John
|
|
|
|
|
Joined: Mar 2008
Posts: 144
OP
Member
|
Interesting link... Pic is a faceless (deadfront) GFI; text reads 'receptacle. Side pics are GFI receptacles. $3.xx(US) ea, 3000 pc minimum. Interesting?
yeah, thats just an example, but you know what i mean, ill put that in the line before it goes out to the shed, would that be OK by code??
-Joe “then we'll glue em' then screw em'” -Tom Silva TOH
|
|
|
|
|
Joined: May 2007
Posts: 169
Member
|
My take on sheds is that in most cases they are not permanent structures. Sure they might never move once installed, but they might.
I consider them a plug-in appliance. I pipe to a bell box on a post near the shed with a GFI receptacle and a bubble cover installed. Set up the shed with a WP pigtail and plug it in.
|
|
|