25 KVA Transformer grounding #186569 05/19/09 03:23 PM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Would it be OK to run the grounding electrode conductor for a 25 KVA 3 phase 480-208Y/120V transformer to the existing service ground in the adjacent switchgear? The only accessible building steel is bolted together lattice trusses(not a reliable ground)and the water entrance piping is not in the vicinity? Driving a ground rod would be extremely risky due to existing unknown substructures.

2017 / 2014 NEC & Related Books and Study Guides
Re: 25 KVA Transformer grounding [Re: wewire2] #186577 05/19/09 09:14 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
I'd say read 250.30 A(7)
Exception # 2.
2005 N.E.C.

Re: 25 KVA Transformer grounding [Re: Yoopersup] #186584 05/20/09 02:57 AM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Good advice,thank you. I skipped right over that exception in my quest for the answer. The transformer is fed from a subpanel that is fed from the switchgear. I guess the next step is to verify whether the subpanel is suitable for use as service equipment.
Now I'm wondering what criteria the manufacturer must abide by in having their product listed as suitable for use as service equipment.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
277,312 Are you busy
211,119 Re: Forum
198,142 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3