Temperature Derating #186203 04/27/09 03:48 AM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Hey y'all. Been a while since I was here. Hope someone can un-confuse me. confused

Problem:
Currently using #10 THWN, protected by a 20-amp breaker, for a run from the house to a residential greenhouse. I'm using the #10 in this case for Voltage drop. Once at the greenhouse, however, I was planning on switching to #12 THWN for branch circuit. My question is about derating the wire once it is inside the higher ambient temperature of the greenhouse. Assuming the temperature will be higher enough to warrant derating, would I have to derate to the point of having the circuit on a 15-amp circuit? If so, what are the ramifications, if any, of having my #10 on a 20-amp breaker?


2017 / 2014 NEC & Related Books and Study Guides
Re: Temperature Derating [Re: Tripp] #186205 04/27/09 04:06 AM
Joined: Jul 2004
Posts: 9,604
G
gfretwell Online Content
Member
How hot is the greenhouse? Bear in mind you derate from the 75c column so until it gets up in the 130f range you should be OK with 3 wires in the pipe/cable.
If this is an agricultural greenhouse I doubt it really gets over 100 before the plants burn up. If it is a solar collector greenhouse you need the design temp.


Greg Fretwell
Re: Temperature Derating [Re: gfretwell] #186207 04/27/09 08:46 AM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Thanks for the quick reply, George. My mistake, I guess, was in using the 60 degree column. But now I see from the examples in NEC2008 Handbook for derating per article 310.15 that they actually use the 90 degree column (though this is for number of conductors in conduit). I can't find which column to use for temperature correction. Can you help me out with a code reference for using the 75 degree column? Much obliged.


Re: Temperature Derating [Re: Tripp] #186211 04/27/09 11:35 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
The principle holds ... assuming the wire is a 90 degree rated type, you do ALL your derating starting from the 90 degree column. Looking at the temperature limitations of your terminations is the last step in the process.

Re: Temperature Derating [Re: renosteinke] #186213 04/27/09 12:50 PM
Joined: Jul 2004
Posts: 9,604
G
gfretwell Online Content
Member
The derating info is in the table at the bottom of 310.16.
The only reason I said 75c was if you are using THHN/THWN in a wet location you should use the THWN rating to be totally code compliant. I thought the greenhouse might be wet.
If this is single rated THWN you have to use 75c


Greg Fretwell
Re: Temperature Derating [Re: gfretwell] #186219 04/27/09 04:48 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
I was looking at THWN[size:8pt]-2, (90 degree column), but I can see that the temperature in the g'house will not be a continuous 90 degreesC. Nevertheless, "Reno" sez always begin derating from the 90 degree column.

"Reno": how come? Code reference please. Thanks.[/size]

Re: Temperature Derating [Re: Tripp] #186220 04/27/09 06:06 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
I think since you are using THWN-2 you are starting at the 75 column. If you were using THHN-2 then you'd be starting from the 90 column. The ambient temperature apparently is not an issue. By the way, don't call Greg, George, he might get insulted:)


George Little
Re: Temperature Derating [Re: George Little] #186223 04/27/09 09:21 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
"By the way, don't call Greg, George, he might get insulted:) "

Holy Toledo! Humble apologies to all parties involved!! eek

- Tripp

Re: Temperature Derating [Re: Tripp] #186224 04/27/09 09:27 PM
Joined: Jul 2004
Posts: 9,604
G
gfretwell Online Content
Member
No problem here, I am honored to be confused with George L.


Greg Fretwell
Re: Temperature Derating [Re: Tripp] #186225 04/27/09 09:33 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
[size:11pt]THWN -2 is clearly listed under the column for 90 degree.
[size:8pt]
Still no one is giving me a code reference.

The only thing I "know" about which column to use for what situation is that for NM you use the 60 degree column if the amperage is 100a or less; and the 75 degree column for NM over 100a. And the only reason I "know" this is that it is written in my 5th -yr. codebook, per my instructor at the time, in preparation for the big exam.. I have no idea where he got this.

Besides, none of that helps me with the question of where in the code does it specify which column to use for derating. You may be forcing me to dig out old study aids from the musty bins of my garage.
[/[/size]size]

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 74
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 15
Admin 8
Popular Topics(Views)
278,689 Are you busy
211,887 Re: Forum
198,939 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3