New to gas stations #185974
04/08/09 10:27 PM
04/08/09 10:27 PM
L
leland  Offline OP
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Hi All!

Got a simple problem and a simple fix.

1 conductor is broken between the JB and the pump.
This conduit 'LBs' out of the building to an EY fitting,then to the pump Manhole. There is an inline fitting,similar to an 'EY' there (just before entering the JB for the pump). Not a problem.

What is the best way to get all the packing and sealant out of these fittings? And re-loading the 'inline' fitting? So as to facilitate a quick easy pull.

This is on the load side of all controls,Pump feed only.

Thanx, Lee

Work Gear for Electricians and the Trades
Re: New to gas stations [Re: leland] #185975
04/08/09 10:50 PM
04/08/09 10:50 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
You need to .... cry laugh

You use a drift pin (long skinny punch or rod) and a hammer to break up the sealant. Sweep / vacuum / blow the bits out, replace all the wires, and replace all the seal materials.

If circumstances permit, you can cut the pipe, instal rated unions, and just replace the seals. complete.

One nice, "un-listed" use for the EY fittings is as a place to add wire lube for your pull.

Re: New to gas stations [Re: leland] #185976
04/08/09 11:22 PM
04/08/09 11:22 PM
L
luckyshadow  Offline
Member
Joined: Jan 2005
Posts: 315
Maryland USA
There is no easy way. If the sealant was installed properly there is a real good chance you will damage the conductors in the conduit as you chip out the sealant. I would first try to chip it out and see how much a PITA that is. If that proves to be a pain I would look into listed,approved unions and a new fitting and just cut the conduit pull out the conductors, fix the conduit ,pull in new conductors, and reseal.

Re: New to gas stations [Re: luckyshadow] #185977
04/08/09 11:45 PM
04/08/09 11:45 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,252
Estero,Fl,usa
Gee I was waiting to hear a trick wink


Greg Fretwell
Re: New to gas stations [Re: luckyshadow] #185978
04/08/09 11:53 PM
04/08/09 11:53 PM
L
leland  Offline OP
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
HOLLY CRAP!!!!

If it's that much trouble why don't we require multiple conduits to each location?

So I assume it aint a 'shut down the pumps for 3 hours' deal?

HOLLY CRAP (oops I stated that already)

I got a 'JB' in the building,then an 'LB' down,'EY'. The inline wich-a-ma-callit- and the pump 'JB'.
Maybe 30' Tops!!

A great friends brother (I may add I have not paid for auto repair in 10 yrs).

HOLLY CRAP!!!

There has to be another option than re-pipping,and a total upgrade. This ,I'm sure, is not the first conductor to fail in a filling station.

It is 3/4 conduit with 2-220V ckts. not a problem to pull in ALL new conductors. But why should it become a 'Project'?

Re: New to gas stations [Re: leland] #185979
04/09/09 12:04 AM
04/09/09 12:04 AM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,252
Estero,Fl,usa
Do you have the tools to thread pipe? If you can get in there you could cut it off and rethread the pipe I suppose. Easier than eating up the driveway to run new pipe.
If you were lucky there would be a coupling below the sealoff.


Greg Fretwell
Re: New to gas stations [Re: gfretwell] #185981
04/09/09 08:28 AM
04/09/09 08:28 AM
L
leland  Offline OP
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
I will have them on hand (threaders).
Another thought,to avoid down time. How about if I temp out the pumps with NM? The round box at the pumphead,this way the pumps can still operate.

Only catch,the conduit IS the ground.

Think I'm looking at a regular shut down.
Thanx Guys. Sorry for the 'bone head' dilemma.

Re: New to gas stations [Re: leland] #185986
04/09/09 10:35 AM
04/09/09 10:35 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 947
Chicago Illinois USA
You can do that if you can find NM that's rated for use in a Hazardous environment.

Besides, temporary fixes tend to never get done right. As soon as things are jerry-rigged to run, the urgency to getting the thing fixed correctly just sort of goes away. Just look at some of the 'temporary' horror stories on this board.

Those sealing fittings were not designed to have the stuff chipped out of them, so it's a royal PITA to do that.
I think you're stuck replacing the fitting unless you want to spend a lot of grunt work chipping and vacuuming.


Ghost307
Re: New to gas stations [Re: ghost307] #185989
04/09/09 12:44 PM
04/09/09 12:44 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
Maybe you'll get lucky and whoever sealed them first packed the pipe with DuxSeal to keep the compound from running too far into the pipe. I see that around here all the time and it sure makes it easier to break it out.


---Ed---

"But the guy at Home Depot said it would work."
Re: New to gas stations [Re: EV607797] #185990
04/09/09 01:23 PM
04/09/09 01:23 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Just in case you haven't dealt with this stuff before, here are the main ways Mr.Murphy can complicate things:

1) First, it's not unheard of fo the seals to have never been sealed. Oops! In that case, thank heaven, and simply pull out the bad wires. Then pack the seals properly.

2) Often the fiber dam fails, resulting in the mortar-like sealant running down into the pipe, and setting up in some low spot. Shovel time! You get to dig up the pipe, usually to the first sweep.

3) Other times the rigid pipe will corrode, with flakes of rust or collapsed pipe making a new pull impossible. A related problerm - which might be the cause of your bad wire - is when compacting and paving operations break (or crush) the pipe.

4) Often, there is not enough room between pipes for you to cut or thread the old pipe in place. Again, in that case, you're best served by digging down to the sweep, and working down there.

When you do finally getyour new wires in, do yourself a favor, and pull in a few extras; this will -maybe- save the day in the event another wire goes bad.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,618 Are you busy
186,361 Re: Forum
175,819 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 16 (0.005s) Memory: 1.0273 MB (Peak: 1.2094 MB) Zlib enabled. Server Time: 2018-08-19 04:24:59 UTC