Pool bonding and grounding #185826
03/31/09 08:48 AM
03/31/09 08:48 AM
H
harold endean  Offline OP
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Does anyone out there certify pool bonding and grounding? If so, (Just out of curiosity) what kind of tester is used? I heard that there are several types of testers, but don't know which ones are used. Someone also told me that you need a length of #8 copper that is tested to show same exact resistance for each test. I also heard that the type of meter used puts out a small amount of voltage while it is being used for the test. Thanks!

Work Gear for Electricians and the Trades
Re: Pool bonding and grounding [Re: harold endean] #185828
03/31/09 09:05 AM
03/31/09 09:05 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,926
Brick, NJ USA
Harold:
A flashlight with a plug-in tail for 'continuity test'
LMAO

Seriously, a ground resistance tester (I believe that's the correct term for the device) is used by a few guys here.

IF I get a chance, I'll ask one of them





John
Re: Pool bonding and grounding [Re: HotLine1] #185831
03/31/09 12:13 PM
03/31/09 12:13 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,182
Estero,Fl,usa
You could verify that there was some bonding going on with a VOM but that might not prove all the required attachments were done. You should see virtually zero ohms between all the exposed metal that is required to be bonded but I am not sure how you absolutely prove all the embedded steel was. That is why the visual inspection is so important before the concrete guy shows up.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 222
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,084 Are you busy
181,127 Re: Forum
171,323 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.011s Queries: 15 (0.003s) Memory: 0.9509 MB (Peak: 1.0782 MB) Zlib enabled. Server Time: 2018-02-25 15:46:19 UTC