#185826 - 03/31/09 09:48 AM Pool bonding and grounding  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Does anyone out there certify pool bonding and grounding? If so, (Just out of curiosity) what kind of tester is used? I heard that there are several types of testers, but don't know which ones are used. Someone also told me that you need a length of #8 copper that is tested to show same exact resistance for each test. I also heard that the type of meter used puts out a small amount of voltage while it is being used for the test. Thanks!


Work Gear for Electricians and the Trades

#185828 - 03/31/09 10:05 AM Re: Pool bonding and grounding [Re: harold endean]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,857
Brick, NJ USA
Harold:
A flashlight with a plug-in tail for 'continuity test'
LMAO

Seriously, a ground resistance tester (I believe that's the correct term for the device) is used by a few guys here.

IF I get a chance, I'll ask one of them





John

#185831 - 03/31/09 01:13 PM Re: Pool bonding and grounding [Re: HotLine1]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,103
Estero,Fl,usa
You could verify that there was some bonding going on with a VOM but that might not prove all the required attachments were done. You should see virtually zero ohms between all the exposed metal that is required to be bonded but I am not sure how you absolutely prove all the embedded steel was. That is why the visual inspection is so important before the concrete guy shows up.


Greg Fretwell


Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.003s) Memory: 0.7530 MB (Peak: 0.8792 MB) Zlib enabled. Server Time: 2017-08-17 09:53:04 UTC