T
Member
I have a commercial garage, that was done by an unlicensed electrican, without permits and was caught. So I get to be clean up guy. Clean up is going well except for this one issue that has me scratching my head...

"Provide fault current data & calculations & arc flash incident energy at working distance calculations at site for electrical inspection purposes."

This is just a plain repair shop. Plugs, lights, 2 lifts and me with no idea how to do these calculations.:)


Shake n Bake
Horizontal Ad
Joined: Apr 2002
Posts: 7,408
Likes: 7
Member
Trick:
You can get some info on KAIC calcs at:

http://www.bussman.com/2/CooperBussmannLiterature.html

The 'SPD' and 'Plan Review' items provide a basic intro to
fault current calcs; point to point method.

The literature used to be 'free'; now I see 'purchase'. I have a few of these; 'either 02 or '05, if you're not in a big rush. PM me if you want.

The flash boundry calcs are not something I know how to do; I think it's best left to an engineer.

Why does the AHJ want all the calcs?


Last edited by HotLine1; 03/04/09 05:43 PM.

John
Joined: Dec 2000
Posts: 4,294
Member


You can calculate the fault current available with this calculator from Siemens:

https://www.sea.siemens.com/consultant/docs/DA_SC_Calculator_V1.1.xls

You'll need to know the serving transformer's voltage, size and impedance, and the length, size, and conductor material of the feeder.


Joined: Aug 2005
Posts: 251
T
Member
Thanks for the info and the calculator.

Originally Posted by HotLine1
Trick:

Why does the AHJ want all the calcs?



I think thats the owners reward for not hiring a contractor and pulling permits. That and some additional inspection hours hes charging him for inspections.



Shake n Bake
Joined: Jan 2004
Posts: 1,507
G
Member
Good Luck on getting the Available Fault current information on the transformer from the utility. They quit giving that out. "In the interest of saving money" Talk to Darrick.


George Little
Joined: Aug 2007
Posts: 853
L
Member
Originally Posted by Trick440
Thanks for the info and the calculator.

Originally Posted by HotLine1
Trick:

Why does the AHJ want all the calcs?



I think thats the owners reward for not hiring a contractor and pulling permits. That and some additional inspection hours hes charging him for inspections.



Funny how that works! perfectly legal as well! smile

I have never been asked for such information and have yet to find anyone who understands the new 70E statutes.

Misconceptions abound.I try,my head spins and off I go...Oh well.

Joined: May 2005
Posts: 984
Likes: 1
G
Member
Here in ComEd territory the biggest 208V transformer that you can get from them is 750KVA. We just assume the fault current based on that and call it good we you can't get the actual value from the local utility.


Ghost307
Horizontal Ad
Joined: Dec 2002
Posts: 339
S
Member
You may be able to use the generic information for the arc flash hazard analysis if you meet all the requirements in NFPA 70E 130.3 exception #1. Otherwise you need an Electrical Engineer who has done the calcs before. The fault current used by assuming infinite source before the transformer (as for figuring minimum AIC rating for equipment) may easily leave you under protected during arc fault (see printed info from people such as Peter Walsh and Jim Phillips).


To do the AIC calculations, the above information is good.


Last edited by sabrown; 03/03/09 12:08 PM.
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Originally Posted by HotLine1
Trick:
You can get some info on KAIC calcs...


Allow me to be picky. The correct phrase is "you can get some info on SCA calcs...".
AIC means Amps Interrupting Capacity - this is a rating supplied by the manufacturer you can not calculate it. It is only available by testing.
SCA is Short Circuit Amps - this is what you calculate.
SCCR is Short Circuit Current Rating - this equipment rating can be determined in the field.
NEC 110.9 and 110.10 require that your equipment be rated for the available SCA.

If you want an entire copy of the Bussmann 2008 SPD you have to pay for it. However I have found that you can download the individual sections, one at a time, for free.

Joined: Apr 2002
Posts: 7,408
Likes: 7
Member
JBD:
OK, you are allowed to be picky!

SCA that you calc result in a shall we say amperage figure that you use to determine the AIC of the buss bracing, and the OCP; right?

Based on the above I used the term KAIC, which is the basic end result of the calcs.

Perhaps my bad choice of terms.




John
Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,685
Joined: October 2000
Top Posters(30 Days)
Popular Topics(Views)
333,639 Are you busy
259,012 Re: Forum
240,428 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5