Im rewiring a 100 year old home that has 100 amp pushmatic panel in it. Im temporarily tighing in a 20 amp circuit in for a bedroom.
Im pretty sure i have the answer to this question but want to make sure. I tighed in the new 20amp circuit but the breaker was off i then turned the main breaker back on and heard a pop sound so i quick shut the main off again.
I forgot to turn off alot of the branch circuits before i turned the main back on so was that the pop i heard because of the load? There was nothing on in the house just the fridge and the lights in the basement.
I first thought there was a short in the circuit i just ran because i had to use wiremold thinking i chafed a wire. I only hooked the circuit up to the breaker and the neutral to the ground bar i never turned the circuit breaker on so i dont see how that is the problem.
So was this pop sound because of the fridge and light loads? Nothing was burning or smelled burnt in the panel.
So at the end i turned off all the branch circuits and then turned the main on then each branch circuit without any pop noise.
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
I'd venture a guess that you heard the breaker mechanism closing.
The pushamatics make 'odd' noises occasionally. Some guys call them 'pop-o-matics'
John
|
|
|
|
Joined: Dec 2005
Posts: 152
Member
|
Does tighed = tied and tighing = tying, not trying to be smart just want to make sure I understand your post. I assume you're getting it inspected right?
|
|
|
|
Joined: May 2003
Posts: 1,158
Member
|
I think he meant tying in
|
|
|
|
Joined: Aug 2007
Posts: 853
Member
|
Where is Ohia?
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Don't they require AFCI's in Pennsylvania in bedroom circuits?
I don't think they make a Pushmatic AFCI.
|
|
|
|
Joined: Nov 2005
Posts: 6
OP
New Member
|
Sorry yes i meant tying haha. I remember winning awards for spelling back when i was in school now i cant spell for **** ha.
Anyway still don't know what that pop sound was but everything works nothing is burnt. But when i finally turned the 20 amp breaker on for the circuit i ran it tripped right away. Turned out i smashed a wire putting on the internal 90 cover on the wiremold! I hate wiremold!
Anyway case closed everything is fine and dandy now haha.
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
That's over!
Leland: Think she means Ohio?
John
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
"Pop" always meant that an arc either welded or blew open, to me. I am not sure where it happened in that can but that's what happened. Maybe that is just the way Pushmatics close the circuit. Never saw one.
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
Greg: They were made orig by 'Bulldog', then later I believe ITE bought the brand/design. I used to have a bunch of then in the shop, single, double and three pole.
IMHO, they were a pain in the butt. Bolt-in, tight panel space, and I wonder if they ever had a SWD rating.
It was 'push-on; push-off' with an indicator in the 'push' part.
John
|
|
|
Posts: 4,116
Joined: October 2000
|
|
|
|
|