Split systems #184751
02/20/09 01:52 PM
02/20/09 01:52 PM
H
harold endean  Offline OP
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
When you have a split system HVAC unit, where the air handler mounts on a wall in the room (sometimes over the door.) and the compressor is outside. We know that the compressor needs a disconnect, what about the air handler? Do they have a built in disconnect switch inside of the unit? What if there isn't one, do you need one? What if the circuit breaker is lockable, would that count as a disconnect?

2017 / 2014 NEC & Related Books and Study Guides
Re: Split systems [Re: harold endean] #184752
02/20/09 02:02 PM
02/20/09 02:02 PM
L
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Yes the AH would need a disconnect.
Most of these that I have done have the switch built in (Sanyo).Both 120 and 240 V models.

The breaker would still need to be 50' and With in site.

Re: Split systems [Re: leland] #184753
02/20/09 06:11 PM
02/20/09 06:11 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
The air handler in mine is low voltage, wired with thermostat wire. I assume the disconnect is the plug.
I think I have bigger fans in my PC case. It is about an amp at 24v as I recall. The condenser is 120v listed for a 15a circuit. I put it on the service outlet for my real AC.


Greg Fretwell
Re: Split systems [Re: gfretwell] #184754
02/20/09 06:22 PM
02/20/09 06:22 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
I just looked at the installation guide and they do not show a disco for the AH

http://us.lge.com/download/product/file/1000001368/Service%20Manual_LS092HE_MFL32351801.pdf



Greg Fretwell
Re: Split systems [Re: gfretwell] #184762
02/20/09 09:59 PM
02/20/09 09:59 PM
P
pdh  Offline
Member
Joined: Jan 2005
Posts: 354
My electric water heater on its own 240V 30A circuit, rated 4500W, does not have any disconnect other than the breaker itself. It is hardwired without a plug. Does it need any more of a disconnect? I don't see how this would be any different than the air handler part of the AC, as long as it is at least on its own circuit.

Re: Split systems [Re: pdh] #184765
02/20/09 10:42 PM
02/20/09 10:42 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
If your referring to a mini-split AC system, all of the systems I have seen for probably the last 15-years get power for the indoor evaporator blower and controls from the terminal board in the outdoor condenser.
When you pull the disconnect for the outdoor unit, you also kill power to the indoor unit. I would say that unless you see a requirement for a separate disconnecting means for the indoor unit in the manufactures listed instructions for that particular equipment, you shouldn't need one.

Re: Split systems [Re: pdh] #184768
02/20/09 10:51 PM
02/20/09 10:51 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
Electric Water Heaters come under Appliances (422.13).Article 422
Cannot have a Plug for a Disconnect unless its portable (422.1 & 422.16) & does require a Disconnect either Within Sight OR capable of being locked (422.30 & 422.31).

Motors AHU's ect come under Article 430.
Start with 430.101 & 430.102 (A) & 430.102(B)
They do require disconnect switches per theses sections.
430.109 Types of Disconnect switches Approved for use as stated.
Except under the exceptions as noted.

Re: Split systems [Re: KJay] #184769
02/20/09 10:55 PM
02/20/09 10:55 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
You want to look at Article 440, Air Conditioning equipment. Specifically, 440.14.

The disconnect - which CAN be a plug - has to be within sight of the equipment. Now, some might quibble, but to me, this means that the disconnect for the equipment you're working on has to be within sight of that equipment. In other words, if the system has components in more than one location, each location needs another disconnect.

BTW, a point of vocabulary: the part we are discussing is called the 'evaporator.' An 'air handler' is another piece of gear completely. The part outside is called the 'condenser,' and contains the compressor.

Re: Split systems [Re: renosteinke] #184772
02/20/09 11:16 PM
02/20/09 11:16 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
430.109 does list a Cord & Plug as a approved disconnect . I stated see 430.109 .
440.13 Cord -Connected Equipment
440.12(D) Disconnecting Means Refers you to 440.12
440.14 Location (within sight ) Same as 430.
There is a Exception #1 But for Industral process.
Exception # 2 Might interest you .
440.3 A & B Says 430 applys EXCEPT as modified by 440.

Re: Split systems [Re: Yoopersup] #184776
02/21/09 12:47 AM
02/21/09 12:47 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
These things are close to being 725 class II. I am still looking for the spec on the air handler. It is trivial tho.


Greg Fretwell
Page 1 of 4 1 2 3 4

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,239 Are you busy
189,201 Re: Forum
178,886 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.041s Queries: 17 (0.010s) Memory: 1.0290 MB (Peak: 1.2131 MB) Zlib enabled. Server Time: 2018-12-16 12:50:48 UTC