Transformer bolted to floor #184548 02/12/09 09:18 PM
Joined: Feb 2009
Posts: 1
Powerplay_09 Offline OP
New Member
I had a friend who always bolts his transformers to the floor, but was questioned by another electrician whether it was necessary...we'd like to know if there is a reference in the CEC about having to bolt transformers to the floor or perhaps a building code requirement under "seismic"?

Thanks, any feedback would be appreciated!


Tools for Electricians:
Re: Transformer bolted to floor [Re: Powerplay_09] #185480 03/16/09 02:03 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
Well we don't lean the panels against the wall either. All equipment has to be securly mounted.

The building code defines these things and in a seismic area the rules are stricter often requiring snubbers and seismic rated anchors etc.
2-118 refers us to Appendix G which are the many Building code references.

I can tell you that they must be secured but it surprises me that the rule that says so is not so easy to find and I will be looking.

Re: Transformer bolted to floor [Re: mikesh] #185640 03/21/09 10:59 PM
Joined: Sep 2006
Posts: 111
E
Eddy Current Offline
Member
26-248(1)Transformers of the dry-core open-ventilated type shall be mounted so that there is an air space of not less than 150mm between.............
26-240(4)Transformers shall be protected from mechanical damage.
I'd say either one of those covers it


Last edited by Eddy Current; 03/21/09 11:00 PM.
Re: Transformer bolted to floor [Re: Eddy Current] #185641 03/22/09 12:31 AM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
I carry a hot glue gun just for the purpose of mounting transformers on the floor. It also provides mechanical protection by providing some "give" if a fork lift hits it.

I'm not advocating leaning panels against the wall, but I've seen a few transformers hung by threaded rod from the ceiling and they move quite freely. Sitting on the floor is way more secure - without glue.

The other electrician, in the original post, has a good point. Are there any rules about mounting transformers? What is secure?

Re: Transformer bolted to floor [Re: twh] #185644 03/22/09 12:25 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
If it's suspended by unistrut on threaded rod it's always bolted to the unistrut. If bolting's good enough for the hanging ones it's good enough for the floor mounted ones.


Ghost307
Re: Transformer bolted to floor [Re: ghost307] #185662 03/23/09 05:56 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
Originally Posted by ghost307
If it's suspended by unistrut on threaded rod it's always bolted to the unistrut. If bolting is good enough for the hanging ones it's good enough for the floor mounted ones.

Be careful about that assumption. A transformer hanging from a ceiling might likely survive a seismic event where the one bolted to the floor does not. For example the hole that the bolt goes through can act as a bolt cutter if the hole is larger than the bolt. The side to side motion of a transformer can hammer on the bolt and shear it off. Bolts are much stronger in stretch than shear. the hanging transformer and its suspension will give in a shaker where the bolts on the floor mounted transformer shear off because it is more rigid.

Re: Transformer bolted to floor [Re: mikesh] #185669 03/23/09 09:24 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
Ummmm Then do you Require Large MCC sections or Switchgear to be Bolted to the Floor also?? What if its mounted on Steel Rails like a lot are in Factorys?? Do you then require it be Welded to the rails????

Re: Transformer bolted to floor [Re: Yoopersup] #185673 03/24/09 12:23 AM
Joined: Dec 2000
Posts: 4,287
electure Offline
Member


In California, you'd get a big fat red tag for not bolting down transformers, MCCs or switchgear......

The inspector would probably walk away shaking his head, laughing.


Re: Transformer bolted to floor [Re: electure] #185676 03/24/09 09:25 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
Then in California do they Require Gear WELDED to rails when gears set on them???
Do you know what I mean by metal rails???

Re: Transformer bolted to floor [Re: Yoopersup] #185678 03/24/09 09:40 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
When I was at GE, we'd void your warranty if you didn't bolt down the MCC, Switchboards and Switchgear.


Ghost307
Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 74
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,697 Are you busy
209,620 Re: Forum
196,964 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3