Transformer bolted to floor #184548
02/12/09 10:18 PM
02/12/09 10:18 PM
Powerplay_09  Offline OP
New Member
Joined: Feb 2009
Posts: 1
B.C. Canada
I had a friend who always bolts his transformers to the floor, but was questioned by another electrician whether it was necessary...we'd like to know if there is a reference in the CEC about having to bolt transformers to the floor or perhaps a building code requirement under "seismic"?

Thanks, any feedback would be appreciated!


Tools for Electricians:
Re: Transformer bolted to floor [Re: Powerplay_09] #185480
03/16/09 03:03 PM
03/16/09 03:03 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Well we don't lean the panels against the wall either. All equipment has to be securly mounted.

The building code defines these things and in a seismic area the rules are stricter often requiring snubbers and seismic rated anchors etc.
2-118 refers us to Appendix G which are the many Building code references.

I can tell you that they must be secured but it surprises me that the rule that says so is not so easy to find and I will be looking.

Re: Transformer bolted to floor [Re: mikesh] #185640
03/21/09 11:59 PM
03/21/09 11:59 PM
E
Eddy Current  Offline
Member
Joined: Sep 2006
Posts: 111
Ontario,Canada
26-248(1)Transformers of the dry-core open-ventilated type shall be mounted so that there is an air space of not less than 150mm between.............
26-240(4)Transformers shall be protected from mechanical damage.
I'd say either one of those covers it


Last edited by Eddy Current; 03/22/09 12:00 AM.
Re: Transformer bolted to floor [Re: Eddy Current] #185641
03/22/09 01:31 AM
03/22/09 01:31 AM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
I carry a hot glue gun just for the purpose of mounting transformers on the floor. It also provides mechanical protection by providing some "give" if a fork lift hits it.

I'm not advocating leaning panels against the wall, but I've seen a few transformers hung by threaded rod from the ceiling and they move quite freely. Sitting on the floor is way more secure - without glue.

The other electrician, in the original post, has a good point. Are there any rules about mounting transformers? What is secure?

Re: Transformer bolted to floor [Re: twh] #185644
03/22/09 01:25 PM
03/22/09 01:25 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 947
Chicago Illinois USA
If it's suspended by unistrut on threaded rod it's always bolted to the unistrut. If bolting's good enough for the hanging ones it's good enough for the floor mounted ones.


Ghost307
Re: Transformer bolted to floor [Re: ghost307] #185662
03/23/09 06:56 PM
03/23/09 06:56 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Originally Posted by ghost307
If it's suspended by unistrut on threaded rod it's always bolted to the unistrut. If bolting is good enough for the hanging ones it's good enough for the floor mounted ones.

Be careful about that assumption. A transformer hanging from a ceiling might likely survive a seismic event where the one bolted to the floor does not. For example the hole that the bolt goes through can act as a bolt cutter if the hole is larger than the bolt. The side to side motion of a transformer can hammer on the bolt and shear it off. Bolts are much stronger in stretch than shear. the hanging transformer and its suspension will give in a shaker where the bolts on the floor mounted transformer shear off because it is more rigid.

Re: Transformer bolted to floor [Re: mikesh] #185669
03/23/09 10:24 PM
03/23/09 10:24 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 845
Michigan
Ummmm Then do you Require Large MCC sections or Switchgear to be Bolted to the Floor also?? What if its mounted on Steel Rails like a lot are in Factorys?? Do you then require it be Welded to the rails????

Re: Transformer bolted to floor [Re: Yoopersup] #185673
03/24/09 01:23 AM
03/24/09 01:23 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,271
Fullerton, CA USA


In California, you'd get a big fat red tag for not bolting down transformers, MCCs or switchgear......

The inspector would probably walk away shaking his head, laughing.


Re: Transformer bolted to floor [Re: electure] #185676
03/24/09 10:25 AM
03/24/09 10:25 AM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 845
Michigan
Then in California do they Require Gear WELDED to rails when gears set on them???
Do you know what I mean by metal rails???

Re: Transformer bolted to floor [Re: Yoopersup] #185678
03/24/09 10:40 AM
03/24/09 10:40 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 947
Chicago Illinois USA
When I was at GE, we'd void your warranty if you didn't bolt down the MCC, Switchboards and Switchgear.


Ghost307
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810