why the 125% rule for transformer conductors? #184478 02/11/09 04:03 AM
Joined: Mar 2006
Posts: 81
B
bigpapa Offline OP
Member
Is this conductor derating because of higher temperatures in the transformer?

Tools for Electricians:
Re: why the 125% rule for transformer conductors? [Re: bigpapa] #184490 02/11/09 04:35 PM
Joined: Jun 2007
Posts: 106
M
mr_electrician Offline
Member
Originally Posted by bigpapa
Is this conductor derating because of higher temperatures in the transformer?

No, the 125% is to accomidate the inrush current that happens when a transformer is energized.


Never trust an electrician with no eyebrows!!
Re: why the 125% rule for transformer conductors? [Re: mr_electrician] #184521 02/12/09 09:39 AM
Joined: Sep 2006
Posts: 111
E
Eddy Current Offline
Member
Originally Posted by mr_electrician
Originally Posted by bigpapa
Is this conductor derating because of higher temperatures in the transformer?

No, the 125% is to accomidate the inrush current that happens when a transformer is energized.


Inrush from a transformer? I assumed only motors have an inrush current when energized. I'm going to test that tonite. I have to shut down some power after hours.


Re: why the 125% rule for transformer conductors? [Re: Eddy Current] #184551 02/13/09 01:42 AM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
AC squirrel cage induction motor and transformer are essentially the same, with the motor having the secondary (or rotor) shorted out. I dont think you will see large inrush on a transformer as in a motor unless the transformer is loaded up to its rated KVA.

Re: why the 125% rule for transformer conductors? [Re: jay8] #184567 02/13/09 12:35 PM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
I will disagree on that statement. I have heard the conductors SLAP in the conduit when energizing an unloaded transformer. I believe it is called magnetizing current.

In essence, the inductive reactance of the transformer is zero until the current starts flowing, therefore the transformer looks like a short circuit upon energization. A large current starts to flow, which produces strong magnetic fields, which pushes the conductors away from each other, resulting in the slapping of the conductors against the conduit.

Larry C

Re: why the 125% rule for transformer conductors? [Re: LarryC] #184573 02/13/09 12:59 PM
Joined: Aug 2007
Posts: 853
L
leland Offline
Member
Ive heard that with elevators and other large motors before.

Re: why the 125% rule for transformer conductors? [Re: LarryC] #184578 02/13/09 03:16 PM
Joined: Jun 2007
Posts: 106
M
mr_electrician Offline
Member
Originally Posted by LarryC
I will disagree on that statement. I have heard the conductors SLAP in the conduit when energizing an unloaded transformer. I believe it is called magnetizing current.

In essence, the inductive reactance of the transformer is zero until the current starts flowing, therefore the transformer looks like a short circuit upon energization. A large current starts to flow, which produces strong magnetic fields, which pushes the conductors away from each other, resulting in the slapping of the conductors against the conduit.

Larry C

And that is why we size the conductors 125%. Because of the inrush, not ambient temperature.


Never trust an electrician with no eyebrows!!
Re: why the 125% rule for transformer conductors? [Re: mr_electrician] #184601 02/13/09 11:48 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Rule 26-256 puts the overcurrent at 125%, so the conductor at 125% matches the overcurrent.

Re: why the 125% rule for transformer conductors? [Re: twh] #186118 04/18/09 05:55 AM
Joined: Mar 2006
Posts: 81
B
bigpapa Offline OP
Member
26-258 (3) contradicts any inrush theory. We are allowed to use a 75 kva transformer for example where you would need 60 kva and size the conductors as if you had a 60 kva transformer. Seems that inrush is not considered as long as the overcurrent device does not operate. Not a good design practice sometimes.
Stating that conductors are required to be sized at 125% because it says so in 26-256 is not really answering the question of what exactly are we derating for. I'm sure there is a reason somewhere.

Re: why the 125% rule for transformer conductors? [Re: bigpapa] #186130 04/20/09 01:34 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
It is all to do with ampacity of the load. Transformers are continuous loads and conductors are sized per all other continuous loads. Our electrical equipment is sized this way. It deals with the heating from the conductor on the breaker and the transformer terminals. Conductors are sized to the rating of the transformer and not the O/C device.
You size the conductors for a hot water heater or a lighting load the same way. It sometimes appears a little differently when we say you can only load a 15 amp breaker to 80% but we could think that is the inverse of 125%. In the case of a plug circuit we wire with #14 and the 15 amp wire is only loaded to 80% or 12 amps.
I hope I am making sense.
A 75 KVA transformer is 208 amps at 208 volts the wire must be 260 amps. (75000/208*1.73)1.25 The other way to look at it is what is the largest load than can be connected to 260 amp wire? 260*.8 or 208 amps @ 208 volts 3 phase(75 KVA)


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,184 Are you busy
206,070 Re: Forum
194,081 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3