Switchgear / GFP test #183467 01/10/09 11:42 AM
Joined: Jan 2005
Posts: 315
L
luckyshadow Offline OP
Member
I'm curious of those that install gear that requires Ground Fault Protection by the NEC - How many of you have the GFP tested after installation? Required by 230.95 C ( 2005 nec)

Last edited by luckyshadow; 01/10/09 11:43 AM.
2017 / 2014 NEC & Related Books and Study Guides
Re: Switchgear / GFP test [Re: luckyshadow] #183484 01/11/09 12:33 AM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
Absolutely - It's required by the NEC and the manufacturer. I always ask for the engineers spec on where he wants the trip point, I witness the performance test as administered by the company performing the test and then sign the document that goes on record as compliance with 230.95(C).

For the record, pushing the Test button on the equipment is not acceptable as the "Performance Test"

In my career as an inspector (25 years) I have had 2 systems that did not past the first time.


George Little
Re: Switchgear / GFP test [Re: George Little] #183696 01/19/09 05:01 PM
Joined: May 2007
Posts: 7
B
Brian_John Offline
New Member
We perform secondary injection testing of GFP systems for ECs and over the years (25-28) I have had countless GFP systems fail the initial test.

We test the GFP relay at all factor presets for current pickup and at a timed operation at the settings recommended in the coordination study (if supplied). We also test (megger) the neutral for any grounds downstream of the main service, megger the bus line and load and ductor/micro-ohm the power contacts. Lastly we recommended leaving the main line switch closed (as do manufactures) during construction till power is to be connected and recommended leaving the GFP relay set at minimum current and time delay for minimizing possible damage to equipment during construction.

Last edited by Brian_John; 01/19/09 05:02 PM.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 74
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,697 Are you busy
209,620 Re: Forum
196,964 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3