Water in PVC Conduit #183110 12/26/08 11:06 PM
Joined: Jun 2004
Posts: 613
S
shortcircuit Offline OP
Member
I have a problem with water entering a PVC conduit underground at a poorly glued coupling and it is following the pipe right to an LB in a basement and dripping excessively in the basement.

I was looking for ideas for stopping the water without digging the conduit up.

I thought maybe silicone or some sort of expanding waterproof foam.

Any Ideas?

Thanx,

shortcircuit

Work Gear for Electricians and the Trades
Re: Water in PVC Conduit [Re: shortcircuit] #183111 12/26/08 11:43 PM
Joined: Jul 2002
Posts: 8,379
Trumpy Offline
Member
Only way you are going to fix that properly is dig it up and repair the bad joint.
Gluing conduits is 1st year apprentice stuff, especially if they are laid under-ground.
I wouldn't go down the road of sealing the conduit up, it screams of handyman workmanship.
BTW, what size is the PVC conduit?

Re: Water in PVC Conduit [Re: Trumpy] #183116 12/27/08 08:49 AM
Joined: Jun 2004
Posts: 613
S
shortcircuit Offline OP
Member
The conduit is 1.25...

Digging it up is not an option...

The apprentice is an asset to our industry...jus a PIA when they make a mistake...

I may dig it up outside at the foundation and bring it up and through the sill instead of straight into the basement below grade and arrange the conduit do drain outside.

I thought there may be a sealant that would work to keep the water from entering.

shortcircuit

Re: Water in PVC Conduit [Re: shortcircuit] #183118 12/27/08 09:30 AM
Joined: Jul 2002
Posts: 8,379
Trumpy Offline
Member
With a 32mm conduit, this doesn't sound like a bad joint, leaking that amount of water.
If it was 4 or 6" that might be a different story.
It sounds like there might be a leaking pipe where you came through the wall.

Now don't get me wrong, I'm not taking you to task, shortcircuit, it is easy to blame an apprentice, but at the end of the day, it comes down to the supervisor they have.
If you are going to bury something, make damned sure that all is well BEFORE the trench is back-filled.

Apprentice supervision 101. cool

Re: Water in PVC Conduit [Re: shortcircuit] #183119 12/27/08 09:32 AM
Joined: Aug 2007
Posts: 853
L
leland Offline
Member
whats on the street end? Pole riser with open conduit? It may be there,then duct seal would work.
Been a lot of water around here lately.I would stay away from "damning" it at the house, reroute may be best.

Re: Water in PVC Conduit [Re: leland] #183126 12/27/08 02:25 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
You have to separate what you KNOW from what you THINK.

Our usual glue procedure for PVC conduit does not make for a waterproof joint. We're electricians, not plumbers, so we don't worry about water entry.

This is because water can / does enter the pipe from many other sources ... condensation, boxes, etc.

Pipe should be "arranged to drain." This might involve even putting a weep hole in the side of the pipe at a low spot. Or, replacing that LB with a Tee, for a drain to direct the water whare it won't harm anything.

Mike raised a good point .. are you sure the water is in the pipe, and not just following the pipe through the wall? That is one area that might benefit from some manner of sealing.

Re: Water in PVC Conduit [Re: renosteinke] #183133 12/27/08 07:07 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
Iíve seen this happen with an unsealed conduit in a handhole that was filling with water from rain and melting snow. Duct seal to the rescue?

Re: Water in PVC Conduit [Re: KJay] #183134 12/27/08 09:04 PM
Joined: Feb 2003
Posts: 687
A
Active 1 Offline
Member
One company I worked for had a rule: don't ever penitrate the foundation below grade. If the pipe was brought up above grade to penitrate the building it would not be an issue.


Re: Water in PVC Conduit [Re: Active 1] #183140 12/28/08 12:45 AM
Joined: Feb 2008
Posts: 193
S
schenimann Offline
Member
We wired a house in a development. While leaving one day I passed a outdoor plug on a short post. We had had lots of rain for several days and was raining now. What caught my eye was the water running out of the cover. The water was running out of the plug like a faucet.

I told the contractor/developer to let me know if they wanted it fixed. It would mean a lot of digging.

Like reno said, we're not plumbers. I do work at good connections though. However, this is why code requires wet location wire in conduit in wet locations. Do they make a wet location gfci outlet? smile

Re: Water in PVC Conduit [Re: shortcircuit] #183142 12/28/08 02:43 AM
Joined: May 2005
Posts: 706
T
Tiger Offline
Member
Originally Posted by shortcircuit

I may dig it up outside at the foundation and bring it up and through the sill instead of straight into the basement below grade and arrange the conduit do drain outside.

I thought there may be a sealant that would work to keep the water from entering.

shortcircuit


Rerouting the conduit seems like the best option to me. The only decent water sealant I know is hydraulic cement & that's not a very good option.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,403 Are you busy
209,295 Re: Forum
196,589 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3