#182917 - 12/18/08 01:34 PM Aluminum ser cable temp rating  
sid123456  Offline
Member
Joined: Jan 2005
Posts: 71
Florida
What column do we size ser? Is it 60 c like romex? Or, 90 c which the insulation is rated at?


Work Gear for Electricians and the Trades

#182918 - 12/18/08 02:20 PM Re: Aluminum ser cable temp rating [Re: sid123456]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,105
Estero,Fl,usa
If you are using it for interior wiring rate it like Romex.
338.10(B)(4)(b)


Greg Fretwell