#182650 12/05/08 01:40 PM
Joined: Dec 2001
Posts: 300
M
Member
I'm sitting here reading the tech data sheet for a Siemens type P1 panelboard. I noticed that one of the available breakers listed (Type BGL) has a note #2. Looking at the bottom of the page, note #2 reads:

"Two pole breaker is one phase and neutral, Three pole breaker is two phases and neutral."

What does that mean? I don't have this panel or plan to order it, I just wonder what such a panel would be used for.

Horizontal Ad
Joined: Oct 2006
Posts: 745
E
Member
I has been a long time, but I seem to recall something similar being required for gasoline pumps. I haven't worked with that stuff in years, so don't quote me on that.


---Ed---

"But the guy at Home Depot said it would work."
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
That may be the panel that the AFCI's go into that do NOT come with neutral pigtail, only a load neut/line termination.

Time permitting, I have to read more on this


John
Joined: Jul 2007
Posts: 264
W
Member
Possibly for shunt trip breakers??


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Sep 2002
Posts: 946
Likes: 4
N
Member
It's where a neutral is req. to be switched, and the accessory requires one additional pole space just like a shunt trip.

Joined: Jul 2002
Posts: 680
W
Member
Its a switched neutral 2 or 3 pole breaker, used to break all conductors. Its just a switch on the neutral side as far as I know. Use them all the time in gasoline installs

Joined: Mar 2008
Posts: 9
K
New Member
This breaker is to be used for gasoline pumps or other places where you need to brake the netural also when you turn off the circut

Horizontal Ad
Joined: Jan 2005
Posts: 354
P
pdh Offline
Member
They should just run the pumps on 2-wire 240V and not worry about switching a neutral since there won't be one (at least in North America).


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 812
Joined: April 2004
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
556,594 Are you busy
431,476 Re: Forum
400,904 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5