More than two 15A rated switches on 20A circuits #182388 11/25/08 03:06 AM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
Table 210-21(B)3 allows 2 or more 15 & 20A receptacles on 20A circuits. what does the code say about 2 or more 15A rated switches on a circuit that is protected by 20A breaker?

Thanks for your comments.


Be kind to your neighbor, he knows where you live

2017 / 2014 NEC & Related Books and Study Guides
Re: More than two 15A rated switches on 20A circuits [Re: Niko] #182389 11/25/08 04:08 AM
Joined: Jul 2004
Posts: 9,543
G
gfretwell Offline
Member
Switches are really supposed to be rated for the load so a 15a switch on a 20a circuit is not a problem if it is a 15a (or less load). More of an issue, generally, is whether a switch is motor rated when it is a motor load. You have to watch out for this when you are using a snap switch for things like pool pumps and big "whole house" fans.


Greg Fretwell
Re: More than two 15A rated switches on 20A circuits [Re: gfretwell] #182393 11/25/08 08:52 AM
Joined: Dec 2004
Posts: 329
I
IanR Offline
Member
"Switches are really supposed to be rated for the load"
So what about a 15A switch controlling a duplex receptacle, with a 20A breaker? Where you really can't determine what the load may be.

Re: More than two 15A rated switches on 20A circuits [Re: IanR] #182397 11/25/08 11:55 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
I'ts quite simple, Ian.

Let's assume you have that switch operating a space heater, or other heavy load. The switch simply won't last very long, and stop being a switch. There might not even be any fireworks; the contacts just won't close anymore, and you get to replace the switch.

That's the whole point to the 'motor rating' idea. Motors, and some other loads, require a lot more than the rated current under specific circumstances .... so the switch will need to be able to handle those moments.

Once again, we come up against an example where 'trade practice' has been decades ahead of 'code.' In this instance, I'm referring to the trade proctice of separating the lighting circuits from the receptacle circuits, and using 15 amp circuits for lighting.

Re: More than two 15A rated switches on 20A circuits [Re: renosteinke] #182413 11/25/08 06:09 PM
Joined: Jan 2005
Posts: 354
P
pdh Offline
Member
The one switch failure I ever had was a "failed to OPEN" scenario. But that switch was very much abused.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
272,057 Are you busy
205,954 Re: Forum
194,003 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3