Bonding at the HMBT #182028 11/16/08 12:45 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
Where do you terminate the #8 bonding wire used around the Hydro-Massage Bath Tub (HMBT) if the water circulating pump is double insulated and has no bonding lug on it? I sent in a proposal to terminate it in the J-box of the branch circuit supplying the tub motor.


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Bonding at the HMBT [Re: George Little] #182032 11/16/08 01:56 PM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
They may say that the intent of equipotential bonding does not include tying it to the EGC pointing to the FPN in 680.26(A) but it is not a bad idea. I agree that in a double insulated all plastic installation there is not much to bond. At a certain point I would be asking about the floor. Is it concrete with tile? That may be the next thing to look at if you want to worry about something. That is yet another selling point for the Ufer and bonding the wire in the floor to the rebar in the footer.


Greg Fretwell
Re: Bonding at the HMBT [Re: gfretwell] #182152 11/19/08 07:52 PM
Joined: Apr 2002
Posts: 7,216
HotLine1 Online Content
Member
George:
Did I not read somewhere words to the effect that 'if there is nothing to bond; you're done'??

Double insul motor and PEX piping?
Normal motor with lug, PEX piping (or other brand plastic) with PVC waste??

Going to the panel can create a parallel ground path, con it not?



John
Re: Bonding at the HMBT [Re: HotLine1] #182160 11/19/08 09:56 PM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
What's wrong with parallel grounding paths, we do it all the time, in fact in health care it is required.
In your typical pool installation you have several parallel ground paths. EGC in the underwater light is connected to the bonding grid, as is the case of the pool pump, the cover motor, the heater and any electrical equipment mounted to the screen cage.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,434
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,901 Are you busy
205,763 Re: Forum
193,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3