health care bed receps #180797 09/10/08 05:46 PM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
what is the intent of art 517.18 (A)

moreover the blueprint calls for 2 e-power recep at the bed location 43" AFF this is above the headboard and the second recep at 18" AFF for the bed to plug into.

is the intent to have two receps available for everyday use?
or is it just as it says two branch circuits, practicle or not?

what say you guys?
thanks as always,
H20




Work Gear for Electricians and the Trades
Re: health care bed receps [Re: watersparkfalls] #180800 09/10/08 06:47 PM
Joined: Dec 2000
Posts: 4,287
electure Offline
Member
I'd say the "practicality or not" of 517.18(A) would become apparent when one system failed, and you didn't have the other for backup.
Just as it says.

Re: health care bed receps [Re: watersparkfalls] #180801 09/10/08 06:51 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
It is saying you need receptacles on the normal system and also from the emergency system. If you have outlets of any kind from the normal system on different branch circuits they need to come from the same panelboard.


Greg Fretwell
Re: health care bed receps [Re: gfretwell] #180803 09/11/08 06:10 AM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Be sure to continue reading through 517.18(B) for the number of receptacles and the requirements for how they are served from the circuits in 517.18(A), this may help explain the intent.

Basically there must be receptacles from both the Normal and Critical branches available for use at the bed, this is over and beyond any dedicated receptacles for items such as the bed for example.

As an aside, these must be HG receptacles and they must have an Equipotential of less than .01 ohm per NFPA 99 4.3.3.1.6.2, the meter used should be a medical/bio type analyzer and may be scrutinized closely be the AHJ

Roger

Re: health care bed receps [Re: Roger] #180808 09/11/08 02:32 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
In Florida, after the electrical inspector is done they have an ACHA inspection that enforces everything but NFPA70 and the standard building code.
Those guys are the ones who have the Medical/Bio analyser.


Greg Fretwell
Re: health care bed receps [Re: gfretwell] #180815 09/11/08 04:35 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Originally Posted by gfretwell
In Florida, after the electrical inspector is done they have an ACHA inspection that enforces everything but NFPA70 and the standard building code.
Those guys are the ones who have the Medical/Bio analyser.


They don't need the the analyzer, the installers must show these results, the form must include the meter used, (it used to have to include the last calibration date)location of device tested, path around room, ground reference point, leakage in millivolts, and impedances.

This is true of everywhere I have done hospitals or healthcare facilities including Fl, ACHA was HRS back then.

This is no different than the Isolation Power System commissioning that is required by ACHA, they do not show up on site with the necessary meters and test sets for this either, it must be done or contracted out by the EC doing the project.

You are right that they do not inspect for NFPA 70 but, these requirements are not NFPA 70 requirements.

Roger

Re: health care bed receps [Re: Roger] #180823 09/11/08 08:53 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
That sounds right. I know when I was walking the final with the contractor, engineer and EC they told me what I was looking at was trivial compared to what was going to happen next. My inspections were all just what it looked like, not how it performed.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,453 Are you busy
209,361 Re: Forum
196,636 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3