ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Motion detectors and dimmers
by gfretwell. 09/20/18 04:02 PM
Extension cords
by annemarie1. 09/20/18 08:54 AM
Inspection camera help
by Bill Addiss. 09/19/18 10:50 PM
220/230/240V 60Hz Systems
by gfretwell. 09/16/18 12:37 PM
Acronis Backup 2017
by gfretwell. 09/16/18 12:46 AM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 32 guests, and 24 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
phase failure protection #180730
09/07/08 09:04 PM
09/07/08 09:04 PM
T
tradesmen  Offline OP
Member
Joined: Feb 2008
Posts: 9
shippensburg,pa
I have been called to a church that is having a problem with losing the "b" phase of a 120/208 volt system.This problem has happened 3 times in 2 weeks. Power company had a problem somewhere along the line which was causing the problem,but not at the church though.The church has 3 phase air conditioning equipment and are concerned about damage to the equipment do to low voltage.The service is 3 seperate 400amp fused disconnects,which are located in different parts of the facility.My question is,is there some type equipment that would shut down the power total if a phase is lost.better to have no a/c than run it on partial power
thank you for your in put

Work Gear for Electricians and the Trades
Re: phase failure protection [Re: tradesmen] #180731
09/07/08 09:32 PM
09/07/08 09:32 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Yes, there is. And installing it might be easier than you think.

The newer starters have electronic 'overloads.' Apart from doing what the 'heaters' used to do, they also kick out for low voltage, or a phase imbalance. Motor is thus protected.

The best part? If you can stay with the same make, the new guts will fit in the old enclosures.

Re: phase failure protection [Re: renosteinke] #180733
09/07/08 09:39 PM
09/07/08 09:39 PM
N
NORCAL  Offline
Member
Joined: Sep 2002
Posts: 882
What about a phase failure relay and tie it in to disable the A/C's?

Re: phase failure protection [Re: NORCAL] #180734
09/07/08 11:40 PM
09/07/08 11:40 PM
S
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,335
Alaska
Yep. A phase failure relay has a dry contact on it so it will open the contact. All you need to do is run the control circuit though the contact.


"Live Awesome!" - Kevin Carosa
Re: phase failure protection [Re: NORCAL] #180735
09/08/08 12:02 AM
09/08/08 12:02 AM
J
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 794
Chicago, Il.
I would go with the phase loss monitor (lotsa names for the same thing) as NORCAL suggested. I would also add a Time Delay Operate relay set to at least 5 minutes to prevent short cycling. The PLM looks for phase loss, imbalance, or reversal. A set of contacts from the PLM feed the timer at the HVAC control voltage. This wouldn't be necessary if the controls are already of a smart type that protect compressors. You could drive an indicator from the timer's NC contacts so that building maintenance staff can see that you are waiting for the power to be on long enough before turning on the AC.
Joe

Re: phase failure protection [Re: JoeTestingEngr] #180746
09/08/08 12:11 PM
09/08/08 12:11 PM
J
JValdes  Offline
Member
Joined: Jun 2007
Posts: 301
South Carolina
A phase monitor is the way to go. But do not try to open the service, only the critical equipment like the air.
Use one set of contacts for the alarm.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 7
Popular Topics(Views)
249,352 Are you busy
187,285 Re: Forum
176,636 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.004s) Memory: 0.9771 MB (Peak: 1.1246 MB) Zlib enabled. Server Time: 2018-09-21 20:11:01 UTC