Tamper Resistant Recep. Locations? #180603
09/01/08 06:43 AM
09/01/08 06:43 AM
Z
zapped208  Offline OP
Member
Joined: Feb 2003
Posts: 197
Somewhere in USA
I have to give a price quote for a new log cabin to a builder.
What locations and heights are tamper resistant receps needed?
Don't have a 08 code book.
If builder gets permits now, then I won't have to worry about this since the 08 code here starts Jan 09.
But I would price it with T.P.R. anyway. Thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Tamper Resistant Recep. Locations? [Re: zapped208] #180604
09/01/08 07:50 AM
09/01/08 07:50 AM
W
wire_twister  Offline
Member
Joined: Jul 2007
Posts: 265
Georgia USA
If you are in Georgia you wont have to worry about it then. Georgia did not adopt the tamper proof recept. or the AFCI parts of the 08 code


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Tamper Resistant Recep. Locations? [Re: wire_twister] #180608
09/01/08 10:30 AM
09/01/08 10:30 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Otherwise, I believe that ALL the receptacles are supposed to be tamper-proof ... even the one on the garage ceiling, for the door opener.

BTW ... only a few days remain to offer proposals to the 2011 code.

Correction: Closing date for NEC proposals is November 7, 2008.

A more complete answer:
The code specifies (406.11) tamper-resistant receptacles in ALL areas specified in 250.52.
210.52 addresses receptacles in residences, including: kitchen receptacles, bathroom receptacles, outdoor receptacles, balconies, laundry areas, garages, and hallways.

Oddly enough, as with the AFCI requirements, they seem to have overlooked stairwells.

210.52 makes no distinction of receptacles that are not readily accessible - be they inside cabinets, behind equipment, dedicated (single), or on the ceiling.

One might say the code paints with too broad a brush .... maybe gets into design issues ... well- get those proposals in!

Re: Tamper Resistant Recep. Locations? [Re: renosteinke] #181334
10/04/08 09:21 AM
10/04/08 09:21 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
If you read sec. 406.11 it states that ALL 125 volt, 15 & 20 amp receptacles located as per 210.52 must be Tamper Proof (TP) receptacles. So I guess that garage door receptacles, outlets up high for a TV screen, behind refrigerators, etc., must be TP type.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,252 Are you busy
189,209 Re: Forum
178,892 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.9609 MB (Peak: 1.0939 MB) Zlib enabled. Server Time: 2018-12-17 09:53:59 UTC