I have to give a price quote for a new log cabin to a builder.
What locations and heights are tamper resistant receps needed?
Don't have a 08 code book.
If builder gets permits now, then I won't have to worry about this since the 08 code here starts Jan 09.
But I would price it with T.P.R. anyway. Thanks

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2007
Posts: 265
W
Member
If you are in Georgia you wont have to worry about it then. Georgia did not adopt the tamper proof recept. or the AFCI parts of the 08 code


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Jan 2005
Posts: 5,316
Cat Servant
Member
Otherwise, I believe that ALL the receptacles are supposed to be tamper-proof ... even the one on the garage ceiling, for the door opener.

BTW ... only a few days remain to offer proposals to the 2011 code.

Correction: Closing date for NEC proposals is November 7, 2008.

A more complete answer:
The code specifies (406.11) tamper-resistant receptacles in ALL areas specified in 250.52.
210.52 addresses receptacles in residences, including: kitchen receptacles, bathroom receptacles, outdoor receptacles, balconies, laundry areas, garages, and hallways.

Oddly enough, as with the AFCI requirements, they seem to have overlooked stairwells.

210.52 makes no distinction of receptacles that are not readily accessible - be they inside cabinets, behind equipment, dedicated (single), or on the ceiling.

One might say the code paints with too broad a brush .... maybe gets into design issues ... well- get those proposals in!

Joined: Feb 2002
Posts: 2,233
H
Member
If you read sec. 406.11 it states that ALL 125 volt, 15 & 20 amp receptacles located as per 210.52 must be Tamper Proof (TP) receptacles. So I guess that garage door receptacles, outlets up high for a TV screen, behind refrigerators, etc., must be TP type.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Top Posters(30 Days)
LarryC 2
NORCAL 2
Popular Topics(Views)
291,226 Are you busy
223,730 Re: Forum
209,158 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5