I have to give a price quote for a new log cabin to a builder.
What locations and heights are tamper resistant receps needed?
Don't have a 08 code book.
If builder gets permits now, then I won't have to worry about this since the 08 code here starts Jan 09.
But I would price it with T.P.R. anyway. Thanks

Horizontal Ad
Joined: Jul 2007
Posts: 264
W
Member
If you are in Georgia you wont have to worry about it then. Georgia did not adopt the tamper proof recept. or the AFCI parts of the 08 code


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
Otherwise, I believe that ALL the receptacles are supposed to be tamper-proof ... even the one on the garage ceiling, for the door opener.

BTW ... only a few days remain to offer proposals to the 2011 code.

Correction: Closing date for NEC proposals is November 7, 2008.

A more complete answer:
The code specifies (406.11) tamper-resistant receptacles in ALL areas specified in 250.52.
210.52 addresses receptacles in residences, including: kitchen receptacles, bathroom receptacles, outdoor receptacles, balconies, laundry areas, garages, and hallways.

Oddly enough, as with the AFCI requirements, they seem to have overlooked stairwells.

210.52 makes no distinction of receptacles that are not readily accessible - be they inside cabinets, behind equipment, dedicated (single), or on the ceiling.

One might say the code paints with too broad a brush .... maybe gets into design issues ... well- get those proposals in!

Joined: Feb 2002
Posts: 2,233
H
Member
If you read sec. 406.11 it states that ALL 125 volt, 15 & 20 amp receptacles located as per 210.52 must be Tamper Proof (TP) receptacles. So I guess that garage door receptacles, outlets up high for a TV screen, behind refrigerators, etc., must be TP type.


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Top Posters(30 Days)
Trumpy 5
davey 1
Popular Topics(Views)
551,542 Are you busy
426,066 Re: Forum
396,835 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5