Emergency Circuit Questions NEC 700 #179618 07/24/08 07:07 AM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
building with a generator which has separate emergency transfer switch/panelbd and standby transfer switch/panelboard.
Can the fire alarm system be connected to the emergency system or would it be considered legally required standby power?

A branch circuits for emergency lighting need to run a good distance down a hall which does not have a fire sprinkler system. 700.9(D)(1), assuming it applies to my building, does it apply to branch circuits? If so does anyone manufacture a 1 hour cable or protective system?

2017 / 2014 NEC & Related Books and Study Guides
Re: Emergency Circuit Questions NEC 700 [Re: cgw] #179619 07/24/08 08:26 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Connect the fire alarm wherever you like ... if it's a UL listed control panel / alarm system, it is already required to have, as part of the system, a 24 hr. back-up power supply (ie: big battery).

Re: Emergency Circuit Questions NEC 700 [Re: cgw] #179620 07/24/08 08:58 AM
Joined: Dec 2003
Posts: 751
E
earlydean Offline
Member
Fire Alarm Systems as covered in NFPA 72 require a secondary power supply, not an "emergency source", nor is it classed as a "legally required standby source". Fire alarm secondary power is usually accomplished via batteries. Check out Chapter 4 of NFPA 72.

Only those loads required to be emergency loads are allowed to be connected to emergency sources. (NEC 700.9(B))

So, no, you cannot use an existing emergency source for the fire alarm system.

However, there is not a prohibition for loads cannected to the "legally required standby source".

But, NFPA 72, in section 4.4.1.9.3.1 requires engine-driven generators to comply with NFPA 110, for a Type 10, Class 24, Level 1 System. Type 10 means the generator starts and transfers within 10 seconds. Class 24 means there is enough fuel to operate at full load for 24 hours. Level 1 systems shall be installed when failure of the equipment to perform could result in loss of human life or serious injuries.

And, NFPA 72 section 4.4.1.5.1 requires a four hour battery system if a prime mover provides the power for continuity of service.

So, the bottom line: Use batteries, forget the generator.


Earl
Re: Emergency Circuit Questions NEC 700 [Re: earlydean] #179624 07/24/08 01:01 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
Thanks for the heads up.
We will have battery backup and it looks like the power will be on the standby system vs. the emergency system.

Re: Emergency Circuit Questions NEC 700 [Re: cgw] #179632 07/24/08 09:32 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
I still have the lighting circuits to run down the un-sprinklered hallway. Does anyone manufacture a 1 hour cable or protective system?


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,531 Are you busy
209,423 Re: Forum
196,814 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3