building with a generator which has separate emergency transfer switch/panelbd and standby transfer switch/panelboard.
Can the fire alarm system be connected to the emergency system or would it be considered legally required standby power?

A branch circuits for emergency lighting need to run a good distance down a hall which does not have a fire sprinkler system. 700.9(D)(1), assuming it applies to my building, does it apply to branch circuits? If so does anyone manufacture a 1 hour cable or protective system?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jan 2005
Posts: 5,316
Cat Servant
Member
Connect the fire alarm wherever you like ... if it's a UL listed control panel / alarm system, it is already required to have, as part of the system, a 24 hr. back-up power supply (ie: big battery).

Joined: Dec 2003
Posts: 751
E
Member
Fire Alarm Systems as covered in NFPA 72 require a secondary power supply, not an "emergency source", nor is it classed as a "legally required standby source". Fire alarm secondary power is usually accomplished via batteries. Check out Chapter 4 of NFPA 72.

Only those loads required to be emergency loads are allowed to be connected to emergency sources. (NEC 700.9(B))

So, no, you cannot use an existing emergency source for the fire alarm system.

However, there is not a prohibition for loads cannected to the "legally required standby source".

But, NFPA 72, in section 4.4.1.9.3.1 requires engine-driven generators to comply with NFPA 110, for a Type 10, Class 24, Level 1 System. Type 10 means the generator starts and transfers within 10 seconds. Class 24 means there is enough fuel to operate at full load for 24 hours. Level 1 systems shall be installed when failure of the equipment to perform could result in loss of human life or serious injuries.

And, NFPA 72 section 4.4.1.5.1 requires a four hour battery system if a prime mover provides the power for continuity of service.

So, the bottom line: Use batteries, forget the generator.


Earl
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
Thanks for the heads up.
We will have battery backup and it looks like the power will be on the standby system vs. the emergency system.

Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
I still have the lighting circuits to run down the un-sprinklered hallway. Does anyone manufacture a 1 hour cable or protective system?


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
LarryC 3
NORCAL 2
Popular Topics(Views)
291,350 Are you busy
223,839 Re: Forum
209,239 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5