undersized neutral? #179491
07/15/08 05:03 PM
07/15/08 05:03 PM
S
Sandro  Offline OP
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
New residential service, 600amps. We will be doing the power lines from the transformer to the main disco. Utility says we can run a parallel set of 2-350mcm black and one 4ot white.

Why is the undersized neutral ok?

Tools for Electricians:
Re: undersized neutral? [Re: Sandro] #179493
07/15/08 07:33 PM
07/15/08 07:33 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Canadian Electrical Code Rule 4-022 provides for sizing the neutral. It's a trade practice to reduce by two sizes instead of doing the calculation. For example, a 100 amp service with #3 hots has a #6 neutral.

Re: undersized neutral? [Re: twh] #179519
07/16/08 11:18 AM
07/16/08 11:18 AM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
I'll chime in here. If you decide to reduce the neutral I want calculations and no rule of thumb or trade practice is acceptable in determining the correct size.
Second. If you run parallel in more than 1 raceway then 2 neutrals are going in. 1 for each pipe. See 12-108 for parallel runs. If you can reduce the neutral you can divide the ampacity and install 2 conductors smaller than 1/0 to provide the neutral but there must be a neutral in each pipe as well as bonding conductors if the raceway cannot be used as a bonding method like when using PVC. As stated the rule for reducing neutral is 4-022. Reducing the neutral for resistive 240 volt loads makes sense especially in residential applications where harmonics are almost a non- existent problem.

Last edited by mikesh; 07/16/08 11:20 AM. Reason: add information
Re: undersized neutral? [Re: mikesh] #179550
07/18/08 08:47 PM
07/18/08 08:47 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
A 1000 sq ft house with a full basement, a 12000 watt range and a 6000 watt dryer has a demand of 13500 watts, or 56 amps. It gets a 100 amp service with #6 neutral.

If the same house has an 18 kw electric furnace, it's demand is 31500 watts, or 132 amps. It gets a 200 amp service fed with 2/0 hots. The neutral load is still 56 amps. The ampacity of a 2/0 in a house is 200 amps (note to table 2) and table 17 requires a grounding conductor of 6 awg.

Therefore, this 200 amp service should get a 6 awg neutral.

However, the inspection department has a rule of thumb where they only allow a reduction of two trade sizes, so we must install the larger 1 awg neutral.

I want to do the calculation and install even smaller neutrals. It's in the code.

http://www.codemath.com/cgi-bin/Run.pl?script=Cec8_200

Re: undersized neutral? [Re: twh] #179551
07/18/08 09:34 PM
07/18/08 09:34 PM
W
wacked  Offline
Member
Joined: Dec 2006
Posts: 33
I would have to agree with mikesh, harmonics for residential housing are generally not a issue so a smaller neutral is a way to keep costs down. I must say that a 600 amp service for a residence is on the unique side (big). Maybe you should check and see what kind of "harmonic" loads this installation will be running... a smaller neutral may not be a good idea.

Re: undersized neutral? [Re: twh] #179576
07/21/08 03:55 PM
07/21/08 03:55 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Originally Posted by twh
A 1000 sq ft house with a full basement, a 12000 watt range and a 6000 watt dryer has a demand of 13500 watts, or 56 amps. It gets a 100 amp service with #6 neutral.

If the same house has an 18 kw electric furnace, it's demand is 31500 watts, or 132 amps. It gets a 200 amp service fed with 2/0 hots. The neutral load is still 56 amps. The ampacity of a 2/0 in a house is 200 amps (note to table 2) and table 17 requires a grounding conductor of 6 awg.

Therefore, this 200 amp service should get a 6 awg neutral.

However, the inspection department has a rule of thumb where they only allow a reduction of two trade sizes, so we must install the larger 1 awg neutral.

I want to do the calculation and install even smaller neutrals. It's in the code.

http://www.codemath.com/cgi-bin/Run.pl?script=Cec8_200

Table 17 in BC is #3 Ground for a 200 amp service. No rule of thumb in the code book here.
I take it that table 16 and 17 have changed in Sask since the 2002 code. The new values in the 2006 code were not adopted here.

Re: undersized neutral? [Re: mikesh] #179577
07/21/08 06:56 PM
07/21/08 06:56 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Quote
I take it that table 16 and 17 have changed in Sask since the 2002 code.
We haven't adopted the 2006 but the inspection department has been allowing us to use either. In 2006, Table 18 is gone and table 17 is changed.

If you calculate the size of neutral for every house, I would expect that, in most cases, the neutral would be reduced and in many cases by more than two trade sizes. I've reduced the neutral by two sizes for so many years that I can't imagine not reducing the neutral. Reducing by more than two sizes seems odd, but it must be okay or it wouldn't be in the code.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,201 Are you busy
189,181 Re: Forum
178,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.042s Queries: 15 (0.008s) Memory: 0.9880 MB (Peak: 1.1452 MB) Zlib enabled. Server Time: 2018-12-14 17:04:34 UTC