ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Video door bell causing chime activation of coil
by gfretwell. 12/10/18 12:35 AM
Conduit fill Calculations
by gfretwell. 12/08/18 08:39 PM
Pull out fuse panel?
by Trumpy. 12/06/18 02:12 AM
Swimming Pool question
by HotLine1. 12/05/18 12:37 PM
Tingle off the water spigot
by rmiell. 11/30/18 01:03 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 29 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Need help with service calculation ??? #179040
06/23/08 10:09 AM
06/23/08 10:09 AM
S
site351  Offline OP
Member
Joined: Jun 2007
Posts: 19
Tennessee

Got a question and don't have a code book....

A 3" P.V.C.conduit is ran from under ground transformers
to electric meter packs with 150 breakers. All meter packs
are main lug, no main breaker. Some meter packs contain six
meters and some five, some four. 120/240 volt residential.
I know I can parallel the Pratt 250-250-4/0 alu. in a 3"
p.v.c. pipe...is that big enough to handle the load for
the five and six meter packs ?
6x 150= 900 total amps for the six banger @ 45% = 405
amps ? can't remember how much to derate...
Five meter pack may work with 250...just not sure about the six ... thanks....

2017 / 2014 NEC & Related Books and Study Guides
Re: Need help with service calculation ??? [Re: site351] #179041
06/23/08 11:14 AM
06/23/08 11:14 AM
S
sabrown  Offline
Member
Joined: Dec 2002
Posts: 304
Ogden, Utah, USA
Assuming that you have done calculations on the services and have found that they all are at 150 amps. 5 residential services can be calculated at .45 for a total of 337.5 amps (see 220.84).

6 residential services can be calculated at .44 for a total of 396 amps. Same code reference. Parallel conductor installation of 250 kcmil are good for the 400 amp total (255x2x.8 NEC 310.15(B)(2)(a)) if allowed by your AHJ.

I did not check the nuetral. This also makes the assumption that you meet the multi-residential requirements.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,186 Are you busy
189,168 Re: Forum
178,844 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.004s) Memory: 0.9436 MB (Peak: 1.0559 MB) Zlib enabled. Server Time: 2018-12-13 11:11:28 UTC