#178951 - 06/17/08 06:14 PM Ufer Ground installation  
Up2code  Offline
Member
Joined: May 2007
Posts: 55
Missouri
Hope everyones having great summer! It seems to fly by. My question is how to properly install a UFER ground, aka foundation ground. General contractor pouring foundation on this house says he's never heard of it. We've decided where service(200A single phase) is going on building, but I've never actually installed one. Any info would be appreciated. Thanks!


Tools for Electricians:

#178961 - 06/17/08 11:02 PM Re: Ufer Ground installation [Re: Up2code]  
twh  Offline
Member
Joined: Mar 2004
Posts: 919
Regina, Sask.
Google "ufer ground" with the quotes. There is conflicting information about how it should be done. Such as tied or welded re-bar and about installing bare ground wires in concrete. You might still need the normal ground.


#178963 - 06/17/08 11:27 PM Re: Ufer Ground installation [Re: twh]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Really quite simple. Just run the re-bar from the footings (not foundation) up and out next to the panel (it can go in the foundation walls)(non coated re-bar). Bond that to the panel, done.
That's the simple version... no that's the only version.

The re-bar is now your ground. Anything after that is "supplimental" or bonding.

Last edited by leland; 06/17/08 11:32 PM.

#179014 - 06/21/08 09:18 AM Re: Ufer Ground installation [Re: leland]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,262
Fullerton, CA USA
It's called a concrete encased electrode, and lives at 250.52 (A)(3) in the 2005 NEC.

Quote
That's the simple version... no that's the only version


Well, it's not really the only acceptable version.
____________________________________________________________

......"or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG."

From the period 1942-1960, H.G. Ufer tested 24 buildings in Arizona every 2 weeks for resistance values. The installations consisted of 1/2" steel reinforcing bars encased in the bottom of the footings. As a result of these tests, Ufer recommended that a #4 or larger copper conductor be encased in the bottom of the footings, and further testing be performed. The results of the further testing impressed the members of CMP-5, and the concrete encased electrode was accepted.

The term "Ufer Ground" truly only applies to this copper electrode, but has generally been used for any concrete encased electrode.





#180869 - 09/13/08 11:51 PM Re: Ufer Ground installation [Re: electure]  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,122
Estero,Fl,usa
Make sure your AHJ accepts the turned up rebar method (a piece of rebar above the concrete that is lapped and tied to the steel in the bottom of the footing).
The method that is more universally accepted is a piece of #4 copper tied to the Rebar with a listed clamp and brought all the way to the panel. You always have the fear that this will be broken or stolen between the footer pour and the electrical final though.
In my area of Florida they go with the turned up rebar method and that rebar is in a block cell with a mud ring and cover to keep it accessible.

http://esteroriverheights.com/electrical/ufer.jpg


Greg Fretwell


Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.7710 MB (Peak: 0.9141 MB) Zlib enabled. Server Time: 2017-10-18 05:38:17 UTC