Outdoor hot tubs #178768 06/11/08 12:36 PM
Joined: Dec 2005
Posts: 12
O
Oh Well Offline OP
Member
Hello With regards to spas and hot tubs I'm told that rule 68-404 requires that a means of disconnect in case of emergencies must be located within sight of the tub. Could this possibly be a push button controlling a contactor inside the house? Or would simply using the button to trip the GFI be acceptable? Thanks in advance. Oh Well

Tools for Electricians:
Re: Outdoor hot tubs [Re: Oh Well] #178769 06/11/08 12:46 PM
Joined: Jun 2007
Posts: 106
M
mr_electrician Offline
Member
Originally Posted by Oh Well
Hello With regards to spas and hot tubs I'm told that rule 68-404 requires that a means of disconnect in case of emergencies must be located within sight of the tub. Could this possibly be a push button controlling a contactor inside the house? Or would simply using the button to trip the GFI be acceptable? Thanks in advance. Oh Well


68-404 is talking about a hut tub control box. Usually the hot tub will come with one and located behind a removable cover. If not then the control box can be no closer that 1 meter horozontaly to the hot tub. This is so no one in the hot tub can contact any electrical equipment while sitting in it.

Last edited by mr_electrician; 06/11/08 12:48 PM.

Never trust an electrician with no eyebrows!!
Re: Outdoor hot tubs [Re: mr_electrician] #178798 06/12/08 10:54 AM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
If you are referring to 68-404 (4) A new to the 2006 CEC rule. Then a push-button with a contactor may be acceptable to your inspection department but check first as some jurisdictions won't accept a magnetic contactor as a disconnect. The control button should lock once pressed to ensure the contactor if acceptable won't reclose after you take your hand off the button.
This is for hot tubs and spas located in public locations like a community pool, hotel, or apartment building. You don't have to install this disconnect in a Single family dwelling except perhaps if a bed and breakfast is operating there. The rule came from a couple of entrapment drownings where part of a person or their clothing was trapped in the water inlet and the occupant drowned.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 3
Popular Topics(Views)
275,423 Are you busy
209,311 Re: Forum
196,600 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3