0 members (), 207 guests, and 14 robots.
#178705 06/09/08 10:17 PM
Sandro Offline OP
300 mcm T90Nylon is rated for 295amps. Using the 5% rule, one could use parallel 300mcm runs for a 600 amp service?
Sandro #178706 06/09/08 11:22 PM
twh Offline
If your calculated demand is 620 amps, you can put in a 590 amp service, which would be fused at 600 amps according to 14-104, if a 590 amp fuse is not available. That is, you can install a 590 amp service and fuse it at 600 amps.
twh #178920 06/15/08 10:32 PM
Generally if you are considering applying the 5% rule I would first run it by your local inspector. Yes, it is a rule but doing so makes for a better relationship, especially if you don't know him/her.