#178562 06/04/08 04:07 PM
Joined: May 2003
Posts: 1,158
Member
I get many calls from customers thinking we can just pig tail copper onto aluminum with the proper # 63 marrette. I have always thought it was best to replace the devices with c0/alr devices but i havent seen these in Decora.

Horizontal Ad
Joined: Jan 2006
Posts: 558
R
Member
I dont think there is such an animal as a CO/ALR rated decora device..
A.D

Joined: Apr 2006
Posts: 31
M
Member
Yes I have some on order through Westburn Ruddy, they are purple, chemically treated and allow for different expansion rates or so the sales promo tells me. I thought the was a marrett with a copper tail that was allowed for AL wired homes. I have seen a few homes with AL/CU mixed and was looking for the best way (penetrox and an 833 with a piece of CU takes up space)to help these people out.

Joined: Apr 2006
Posts: 31
M
Member
Sorry, I should have read the question better and I have not seen a AL Decora device.

Joined: Sep 2003
Posts: 200
U
Member
Has anyone seen a Cu/AL pigtail (well-twisted and w/compound) go bad?

I'm curious because to me it seems like as good - or better - a connection than #12 AL wrapped on the screw terminal. Then you don't need to keep AL-rated devices in the truck.

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
I haven't seen many cu/al connections, at all. Has anyone seen a cu/al connection last for 10 or 20 years?

Joined: Apr 2006
Posts: 31
M
Member
Please correct me but isn't that the problem: 10-20 years of mixed metals causing corrosion and heat? I understand that Penetrox should be redone every 5 years (but they say the fixture should be replaced every 5 years)

Horizontal Ad
Joined: Jan 2007
Posts: 22
H
Junior Member
what about split bolts?

Joined: Nov 2007
Posts: 764
K
Member
I know the OP and most of the other posters in this thread are from the great white north, but wanted to chime in anyway.
Last year I switched to the connectors below after learning some unsavory info about those purple wirenuts.
These are listed for CU and AL wires. The only thing is that you will need to buy and use a torque-limiting screwdriver to install them for UL/CSA listing compliance. They can also fill up a device box quickly if you have several splices to make.
The company sent a free sample connector before I purchased in quantity.

Here is the product link. http://www.alcopstore.com/


Joined: May 2003
Posts: 1,158
Member
Originally Posted by KJay
I know the OP and most of the other posters in this thread are from the great white north, but wanted to chime in anyway.
Last year I switched to the connectors below after learning some unsavory info about those purple wirenuts.
These are listed for CU and AL wires. The only thing is that you will need to buy and use a torque-limiting screwdriver to install them for UL/CSA listing compliance. They can also fill up a device box quickly if you have several splices to make.
The company sent a free sample connector before I purchased in quantity.

Here is the product link. http://www.alcopstore.com/



I got the sample also but i have not found a Canadian supplier for them yet

I have a stock of these i use for now.

http://www.tnb-canada.com/en/catalogues/online/comresconstruction/pdf/c5/09_marrcat_e.pdf

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Top Posters(30 Days)
Popular Topics(Views)
333,593 Are you busy
258,964 Re: Forum
240,394 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5