Pig Tailing AL to Copper #178562 06/04/08 04:07 PM
Joined: May 2003
Posts: 1,155
dougwells Offline OP
Member
I get many calls from customers thinking we can just pig tail copper onto aluminum with the proper # 63 marrette. I have always thought it was best to replace the devices with c0/alr devices but i havent seen these in Decora.

Tools for Electricians:
Re: Pig Tailing AL to Copper [Re: dougwells] #178564 06/04/08 05:51 PM
Joined: Jan 2006
Posts: 558
R
Rewired Offline
Member
I dont think there is such an animal as a CO/ALR rated decora device..
A.D

Re: Pig Tailing AL to Copper [Re: Rewired] #178593 06/05/08 10:54 PM
Joined: Apr 2006
Posts: 31
M
marsbar Offline
Member
Yes I have some on order through Westburn Ruddy, they are purple, chemically treated and allow for different expansion rates or so the sales promo tells me. I thought the was a marrett with a copper tail that was allowed for AL wired homes. I have seen a few homes with AL/CU mixed and was looking for the best way (penetrox and an 833 with a piece of CU takes up space)to help these people out.

Re: Pig Tailing AL to Copper [Re: marsbar] #178594 06/05/08 10:57 PM
Joined: Apr 2006
Posts: 31
M
marsbar Offline
Member
Sorry, I should have read the question better and I have not seen a AL Decora device.

Re: Pig Tailing AL to Copper [Re: dougwells] #178618 06/06/08 04:31 PM
Joined: Sep 2003
Posts: 200
U
u2slow Offline
Member
Has anyone seen a Cu/AL pigtail (well-twisted and w/compound) go bad?

I'm curious because to me it seems like as good - or better - a connection than #12 AL wrapped on the screw terminal. Then you don't need to keep AL-rated devices in the truck.

Re: Pig Tailing AL to Copper [Re: u2slow] #178628 06/06/08 09:53 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
I haven't seen many cu/al connections, at all. Has anyone seen a cu/al connection last for 10 or 20 years?

Re: Pig Tailing AL to Copper [Re: twh] #178732 06/10/08 11:08 AM
Joined: Apr 2006
Posts: 31
M
marsbar Offline
Member
Please correct me but isn't that the problem: 10-20 years of mixed metals causing corrosion and heat? I understand that Penetrox should be redone every 5 years (but they say the fixture should be replaced every 5 years)

Re: Pig Tailing AL to Copper [Re: twh] #178736 06/10/08 02:55 PM
Joined: Jan 2007
Posts: 22
H
Hendrix Offline
Junior Member
what about split bolts?

Re: Pig Tailing AL to Copper [Re: Hendrix] #178738 06/10/08 03:31 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
I know the OP and most of the other posters in this thread are from the great white north, but wanted to chime in anyway.
Last year I switched to the connectors below after learning some unsavory info about those purple wirenuts.
These are listed for CU and AL wires. The only thing is that you will need to buy and use a torque-limiting screwdriver to install them for UL/CSA listing compliance. They can also fill up a device box quickly if you have several splices to make.
The company sent a free sample connector before I purchased in quantity.

Here is the product link. http://www.alcopstore.com/


Re: Pig Tailing AL to Copper [Re: KJay] #178739 06/10/08 04:18 PM
Joined: May 2003
Posts: 1,155
dougwells Offline OP
Member
Originally Posted by KJay
I know the OP and most of the other posters in this thread are from the great white north, but wanted to chime in anyway.
Last year I switched to the connectors below after learning some unsavory info about those purple wirenuts.
These are listed for CU and AL wires. The only thing is that you will need to buy and use a torque-limiting screwdriver to install them for UL/CSA listing compliance. They can also fill up a device box quickly if you have several splices to make.
The company sent a free sample connector before I purchased in quantity.

Here is the product link. http://www.alcopstore.com/



I got the sample also but i have not found a Canadian supplier for them yet

I have a stock of these i use for now.

http://www.tnb-canada.com/en/catalogues/online/comresconstruction/pdf/c5/09_marrcat_e.pdf

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,411 Are you busy
209,304 Re: Forum
196,593 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3