ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Happy Thanksgiving
by sabrown - 11/25/20 02:00 PM
Work Gloves?
by sabrown - 11/25/20 01:54 PM
Insulated Tools: A Waste of Money?
by sabrown - 11/25/20 01:52 PM
What does your work place look like?
by Lostazhell - 11/25/20 02:56 AM
Where is Everyone?
by Lostazhell - 11/21/20 04:17 AM
New in the Gallery:
Facebook follies, bad wiring
FPE in Germany pt.2
Who's Online Now
1 registered members (NJwirenut), 20 guests, and 17 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 4 1 2 3 4
Spliced Neutral? #177616 05/08/08 01:11 PM
Joined: Jan 2005
Posts: 61
J
jkochan Offline OP
Member
We opened a panel in our commercial building this morning to trace a few circuits. While in there, I found that one of the neutrals on a branch circuit had been spliced. It is a soldered connection and insulated with what looks like heat shrink tubing. It looks as though a GFCI breaker was removed and a standard 20A breaker installed in it’s place, and they spliced the neutral to reach the bus. Is this legal? Do I have to re-pull this incredibly long branch circuit to correct it or could this be considered a repair to a “damaged neutral”?

Last edited by jkochan; 05/08/08 01:12 PM.
2017 / 2014 NEC & Related Books and Study Guides
Re: Spliced Neutral? [Re: jkochan] #177623 05/08/08 04:37 PM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline
Member
It is perfectly legal to splice a wire in a panel, that being said, solder is not an approved method. Also find out where it goes and why it had GFCI protection to start with. The GFCI breaker was there for a reason, and probably needs to be put back.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Spliced Neutral? [Re: wire_twister] #177654 05/09/08 07:47 AM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
Soldering is an approved method of splicing.

Quote
110.14 (B) Splices. Conductors shall be spliced or joined with splicing devices identified for the use or by brazing, welding, or soldering with a fusible metal or alloy. Soldered splices shall first be spliced or joined so as to be mechanically and electrically secure without solder and then be soldered. All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device identified for the purpose.


As a matter of fact, soldering is one of the only approved methods for some applications.

The exceptions to this are for service conductors (230.81), grounding and bonding conductors where the connection relies solely on solder [250.8, 250.148(E)] and connections to grounding and bonding electrodes [250.70].

Re: Spliced Neutral? [Re: electure] #177658 05/09/08 08:57 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
I think some clarification is necessary.

Solder is a perfectly acceptable method - but not just solder alone. Where solder is used, the wires must have some other means physically holding the wires together - such as twisting them together. Solder will make the 'electrical' connection; the 'mechanical' must come from elsewhere.

Re: Spliced Neutral? [Re: renosteinke] #177663 05/09/08 09:11 AM
Joined: Jul 2004
Posts: 9,541
G
gfretwell Offline
Member
Back in the olden days you made a western union splice and soldered it. You can see why they invented wirenuts.
Assuming this splice was twisted and soldered the thing I might question would be the shrink tubing. Is it "equivalent to that of the conductors". Shrink tube comes in different thicknesses.


Greg Fretwell
Re: Spliced Neutral? [Re: gfretwell] #177666 05/09/08 09:57 AM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
Reno, 110.14(B) needs no clarification.

Quote
Soldered splices shall first be spliced or joined so as to be mechanically and electrically secure without solder

Re: Spliced Neutral? [Re: electure] #177667 05/09/08 11:08 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
Heat shrink does not meet 110.14(B) regardless of thickness, as it is applied after the splice is soldered, vice before. Seems a pretty nitpicky point, though. Is twisting the wires sufficient, though? If so, the heat shrink may only be required to function as electrical insulation. Not sure how you'd check up on that.

Re: Spliced Neutral? [Re: SteveFehr] #177690 05/09/08 06:58 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Steve, I'm not sure I follow you. Tape is a proper means of insulation, and it's certainly applied 'after' the splice is made. I don't have any problem with heat shrink tube as covering for a splice.

I would have a problem is the tube was left with an open end. Otherwise, use it.

For the mechanical connection, twisting the wires is generally enough. Sure, there are exceptions ... where you need to use a hydraulically crimped or welded connection ... but for most purposes, twisting is plenty good.

Naturally, for larger wire (like you might see used in a service), the practice is not to simply try to twist the wires, but rather to braid the strands together. There's an entire art to these splices, that's pretty much been lost.

Re: Spliced Neutral? [Re: renosteinke] #177697 05/10/08 07:29 AM
Joined: Mar 2007
Posts: 101
M
mikethebull Offline
Member
I thought tape was not UL approved to "replace" the original insulation. That was why you have rubber tape and then a outer layer of electrical tape. But why wouldn't the person(s) just have used a wirenut. Seems to me that they must have been "nervous" about electricity, probably a handyman special.

Re: Spliced Neutral? [Re: mikethebull] #177700 05/10/08 10:05 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
All electrical tape, of whatever form, pretty much has to pass the same tests. The only real variable is the voltage rating - and that's based upon only a two-layer thickness.

"Ordinary" electrical tape is listed for 600v. So are the usual splicing tapes and putties. The 'self fusing' nature of the splicing tapes does make the final set waterproof, and the thickness is a real help to building up thickness.

There are reasons for building up some thickness, apart from electrical insulation. For example, to cover sharp edges.

Page 1 of 4 1 2 3 4

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,948 Are you busy
205,833 Re: Forum
193,912 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3