70-E & utility companys #177597 05/08/08 08:11 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
By reading 70-E there not really covered by this even when working on HV switchgear am I right.

Arc Flash PPE Clothing, LOTO & Insulated Tools
Re: 70-E & utility companys [Re: Yoopersup] #177603 05/08/08 09:39 AM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
I am not sure what you mean by you post. 70E is just a standand that was written to "clearify" OSHA requirements. 70E is applicable if adapted by your employer.

In other news, Something I have been wanting to ask you. Going by your user name, where abouts in the U.P. are you Located? I was born and raised as a "Troll". (Michigan humor).


"Live Awesome!" - Kevin Carosa
Re: 70-E & utility companys [Re: sparkyinak] #177629 05/08/08 06:33 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
I forgot to put before the Post Utility Companys.
North of the bridge about 200 miles.

Re: 70-E & utility companys [Re: Yoopersup] #177741 05/11/08 08:45 AM
Joined: Sep 2005
Posts: 120
Z
Zog Offline
Member
Utilities follow NESC, they have been able to dodge 70E for while now but are in the process of adapting many of the 70E rules. They also follow 1910.269 which has many of the same SWP's.

The only thing the 70E brings is the are flash calcs and PPE requirements. The tables only apply up to 38kV and the calcs dont work either, so really they ARE following the 70E, at least the parts that apply.

As far as PPE, linemen have been wearing arc resistant materials for years, but in the substations (Indoor, metal clad switchgear) the current rules the utilities follow are not good enough to protect workers, this is where they SHOULD be following 70E and this is where most of the upcoming NESC changes will apply.

The thing is, an arc flash at 72kV in open air is nothing compared to one at 480V in a cubic box with high available fault currents and a lonfg clearing time like what is found on nearly every 480V substation out there.

I hope I answered your question, if not, please ask a more specific question.


MV/HV Testing Specialist, "BKRMAN"

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,758 Are you busy
209,667 Re: Forum
197,016 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3