In 680.22 (5) Is it the intent of the code to say you do not need gfi protection when a pump motor is 20 ft from inside wall of pool?


dukes
2017 / 2014 NEC & Related Books and Study Guides
Joined: Jul 2004
Posts: 9,662
Likes: 4
G
Member
No, the first part refers to all receptacles within 20' and then it says Receptacles that supply pool pumps shall have GFCI without stipulation of distance.


Greg Fretwell
Joined: Apr 2003
Posts: 139
B
Member
Also keep in mind that all outlets supplying pool pump motors must be gfci protected, whether by receptacle or direct connection in 2008 NEC.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,287
Joined: December 2000
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
282,928 Are you busy
216,696 Re: Forum
203,120 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5