#176733 04/10/08 08:18 AM
Joined: Oct 2002
Posts: 830
S
Member
I was looking over some material I got in the latter part of last year. It is saying that AFCI's are now required to be in most areas of a dwelling, and not just in the bedrooms. Is this something that still is required or has it been amended since?? If it still goes, this is going to increase the cost of wiring quiet a bit. Thanks Steve...

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

sparkync #176734 04/10/08 09:05 AM
Joined: May 2005
Posts: 984
Likes: 1
G
Member
According to the 2008 NEC, whatever isn't GFI will need to be on an AFCI circuit breaker (I've oversimplified somewhat).

When figuring your extra cost...remember that sharing neutrals results in most of these things not working right.

I guess not enough people objected during the NEC adoption process.


Ghost307
ghost307 #176746 04/10/08 05:31 PM
Joined: May 2007
Posts: 47
B
Member
Thats the appeal of the 12-2-2 and 14-2-2 vs the old way of 12-3 or 14-3.


Design-Build isn't supposed to mean design *as* you build.
BryanInBalt #176754 04/10/08 09:21 PM
Joined: Feb 2008
Posts: 193
S
Member
210.12(B) All 120v, single phase, 15 and 20 amp branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms,living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways,or similar rooms or ares shall be protected by afci.
In North Carolina As of July 1, 2008
what is 12-2-2, 14-2-2? Is it 12/3 with an extra nuetral? Do they sell it?

schenimann #176760 04/10/08 11:06 PM
Joined: Aug 2007
Posts: 853
L
Member
2008 NEC + amendments. January, 1, 2008-- Accepted and enforced in Massachusetts.

It's about the only legislation they can seem to get passed and agree on. But thats a good thing. Coz' the other crazy poop they think of aint worth poop.

So in short.. Grid lock is good. " no harm, no foul"!!


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
307,226 Are you busy
235,203 Re: Forum
219,298 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5