Hydro-Massage Bathtub Bonding #176479
04/03/08 07:10 AM
04/03/08 07:10 AM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
The wording in 680.74 is such that only the metal parts associated with the water circulation system need to be bonded together. This would rule out the isolated parts like the faucet or water spout that are quite often metal and are connected to non-metallic piping system. Maybe.

Second point- If we have a double insulated pump there is no bonding needed for the pump and the cord of the pump contains an EGC and grounding of the metallic parts of the pump happens due to the cord/ cap connection to a grounded GFCI protected receptacle. Now, if I choose to terminate the #8 bonding wire to the grounding conductor of the branch circuit, is this a problem?

Last edited by George Little; 04/03/08 07:11 AM.

George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Hydro-Massage Bathtub Bonding [Re: George Little] #176480
04/03/08 08:28 AM
04/03/08 08:28 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,271
Fullerton, CA USA

Re: Hydro-Massage Bathtub Bonding [Re: electure] #176481
04/03/08 08:51 AM
04/03/08 08:51 AM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
The memory is the second thing to go. smile


George Little
Re: Hydro-Massage Bathtub Bonding [Re: George Little] #176483
04/03/08 12:03 PM
04/03/08 12:03 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Originally Posted by George Little
The wording in 680.74 is such that only the metal parts associated with the water circulation system need to be bonded together. This would rule out the isolated parts like the faucet or water spout that are quite often metal and are connected to non-metallic piping system. Maybe.
If the metal fixture is attached to steel or copper pipe, it's grounded through that pipe. If the metal fixture is attached to plastic pipe, it's not a path to ground, and is also safe. Safer, really; there's no chance of something like that becoming energized, so it's not a potential shock risk from that standpoint, either, and is as safe to the bather as if it were plastic.

Makes perfect sense, actually.

Re: Hydro-Massage Bathtub Bonding [Re: SteveFehr] #176543
04/05/08 09:23 PM
04/05/08 09:23 PM
Obsaleet  Offline
Member
Joined: Apr 2003
Posts: 362
Pa
I believe ther is a size of surface area. I think it is in sq inches. X amount of square inches and the bond is needed. I will see if I can find it.

Ob


Choose your customers, don't let them choose you.
Re: Hydro-Massage Bathtub Bonding [Re: Obsaleet] #176544
04/05/08 09:27 PM
04/05/08 09:27 PM
Obsaleet  Offline
Member
Joined: Apr 2003
Posts: 362
Pa
680.26(B)(3) I think applies here

Ob


Choose your customers, don't let them choose you.
Re: Hydro-Massage Bathtub Bonding [Re: SteveFehr] #176556
04/06/08 08:28 AM
04/06/08 08:28 AM
B
BPHgravity  Offline
Member
Joined: Apr 2003
Posts: 139
Port Charlotte, Florida
Originally Posted by SteveFehr
If the metal fixture is attached to steel or copper pipe, it's grounded through that pipe. If the metal fixture is attached to plastic pipe, it's not a path to ground, and is also safe. Safer, really; there's no chance of something like that becoming energized, so it's not a potential shock risk from that standpoint, either, and is as safe to the bather as if it were plastic.

Makes perfect sense, actually.


The requirement in Section 680.74 is to establish equipotential bonding at and directly around the hydro-tub in order to reduce the protential of voltage gradients. It really has nothing to do with grounding or establishing an effective fault path to clear unitentionally energized parts.


Originally Posted by Obsaleet
680.26(B)(3) I think applies here

Ob


Hydromassage bathtubs need only meet the requirements of Part VII. of Article 680. The section you reference would not apply. See Section 680.70


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Re: Hydro-Massage Bathtub Bonding [Re: BPHgravity] #176559
04/06/08 09:59 AM
04/06/08 09:59 AM
Obsaleet  Offline
Member
Joined: Apr 2003
Posts: 362
Pa
I stand corrected however, 680.74 says only the parts that are parts in contact with the circulating water are to be bonded. I would not consider the faucet and handle part of the cirulating system the are the fill system, and are not in contact.

Ob


Choose your customers, don't let them choose you.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,158 Are you busy
185,629 Re: Forum
174,990 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.004s) Memory: 0.9960 MB (Peak: 1.1588 MB) Zlib enabled. Server Time: 2018-07-22 06:38:55 UTC