Yes the series circuit we had had 3 130V 25w lamps. THe firs bulb was brighter than the other 2.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Skeeter #175613 03/05/08 10:05 PM
Joined: Dec 2000
Posts: 4,294
Member
Wasn't the circuit wired in parallel?

Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
Skeeter

Check out these topics in the Technical Reference area:

Basic Circuits #1: Series Circuits

Basic Circuits #3: Ser/ Par + Voltage Divider

Series AC Circuits

Series-Parallel AC Circuits

Many other Schematics, Formulas and similar information may be found in the Tech Reference area.
Click the link below to view the "Menu" page:

Menu For Technical Reference Section

We had a discussion in the Electrical Theory area some time ago, which covered connecting several Incandescent Lamps in Series.

As I remember, there were at least 3 Lamps - each rated for 120VAC, connected in Series.
One Lamp was a lower wattage than the other two - something like One (1) 60 Watt Lamp, in Series with Two (2) 100 Watt Lamps.
The System Voltage used to drive the Lamps was 120VAC.

The preliminary query was why the lower wattage Lamp was brighter than the other two higher wattage Lamps.

The discussion covered basic Ohms Law, which described the reason for the lower wattage Lamp's higher intensity was due to that Lamp's higer Resistance (or since the supply was AC, more correct term would be higher Impedance) - and therefore the 60 Watt Lamp's Filament had a higher Voltage across it.

Since it carried the sum total current of all three Lamps, and had a higher Voltage across it, the highest level of Wattage was transduced in the Lamp with the lower wattage rating - therefore making it the brighter Lamp.

That is the key factor here: the Lamp with the higher Resistance (or Impedance in this case), has the highest Voltage measured across it, and therefore will draw the most Wattage from the Power Supply.

From this example, it should be easy to see why the smaller loads (read most crucial and $$$ loads) lose smoke when an "Open Neutral" situation takes place.

ooooooooooooooooooooooooooooooooooooooooooooooooooooooooooo

In your last reply, you mention that all three Lamps are the same wattage and rated Voltage, yet one is brighter than the other two.

This would mean the one brighter Lamp:

* 1: Might be connected in Parallel,

* 2: Might be of a different rating (wattage and or voltage),

or

* 3: Might have an initially higher Cold Resistance than the other Lamps.

If they are all the same types, and connected in Series, they should all be the same intensity (brightness).

Are they all clear, or is the brighter Lamp clear?
Any of the Lamps Frosted? (non-clear)

Try running the Lamps separately - across 120VAC, and see if the brightness is uniform or not.
If uniform brightness is experienced in the separation test - AND your Series test circuit IS connected correctly in Series, time to look for a good excorcist!!!
wink
Else, adjust accordingly - finding at least Three (3) Lamps with uniform intensity, and verify the test circuit is indeed connected in basic Series fashion - as described below:

*** One side of the 120VAC circuit connects directly to one side of the "first" lamp;
* The other side of the "first lamp" connects directly to one side of the "second" lamp;
* The other side of the "second" lamp connects directly to one side of the "third" lamp;
*** The other side of the "third" lamp connects directly to the other side of the 120VAC circuit.

Basic, Crude ASCII Schematic below:

(120Va)......_(L1)_......_(L2)_......_(L3)_......(120Vn)

Key:
(120Va) = 120VAC Circuit - Ungrounded Conductor
(120Vn) = 120VAC Circuit - Grounded "Neutral" Conductor
...... = Circuit Conductors between Lamps
_(L1)_ = Lamp # 1
_(L2)_ = Lamp # 2
_(L3)_ = Lamp # 3

Please let us know of the outcome

Scott
edited for spelling

Last edited by Scott35; 03/08/08 11:27 PM. Reason: fixed spelling - all hopefully!

Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Apr 2003
Posts: 13
T
Junior Member
Referring to the last post, "ohming them out" after they cool will only tell you if there are working or not (Continuity). The cold filament resistance is significantly less then the resistance it is when its "on". Eg. 120V, 60W bulb draws 0.5 A,--> 120/0.5 = 240 ohms (hot)

Joined: Aug 2001
Posts: 7,520
P
Member
Originally Posted by gfretwell
The best example of this is the old "all American five" tube radio where they had tube filaments ranging from 12v to 50v and they all used 150MA but the effective resistance was selected so they could take 120v line power in series to light them all up.


That was common in Britsh radio and TV equipment of the era too, although with supplies of 200 to 250V the typical table radio with five tubes had to employ a series dropper resistor as well.

In fact the Mullard valve coding system used by tube manufacturers here had the first letter denote the heater characteristics, and some were specifically reserved to designate tubes intended for series connection: P was 300mA, U was 100mA, and so on, the latter being very common on domestic radios of the era (UCH81 converter, UL84 output pentode, etc.).

During the immediate post-war period we imported quite a number of those "All American Five" designs too, modified for U.K. use. One method of adapting the series filament chain for 200-250V was to use a very long power cord which had a nichrome resistance element as one conductor to act as the extra series resistance.

Apparently it worked quite effectively -- Until somebody decided that he didn't like the 9 or 10 ft. cord and tried to shorten it.

pauluk #175819 03/12/08 12:44 AM
Joined: Jul 2004
Posts: 10,053
Likes: 40
G
Member
They had radios in the US with resistor cords too (not AA5). I tried one with with lamp cord and a couple of tubes got real bright for a second.