load diversity factor for car parking lift #175259 02/25/08 09:40 PM
Joined: Feb 2008
Posts: 12
T
theseus Offline OP
Member
I have 50 car parking lifts,each is 2.2kW.I want to know how to calculate the feeder size and the breaker size.

Thank you.

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: load diversity factor for car parking lift [Re: theseus] #175262 02/25/08 11:10 PM
Joined: Sep 2002
Posts: 908
N
NORCAL Offline
Member
You don't provide much info, like voltage, # of phases....

Re: load diversity factor for car parking lift [Re: NORCAL] #175266 02/25/08 11:32 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Since lifts are little more than a motor, I would apply the usual motor rules. I believe that your situation is covered in 430.24, exception 1.

Still, I would not carry that exception to an extreme. One does need to make a judgment call as to how often the lifts will operate, and how many will operate at once. For example, the pattern of use will differ between a transmission shop, a tire shop, and a school shop.

Indeed, this might be a good time to review the 'tap rules,' and plan your distribution accordingly. Here is where the importance of a fusible disconnect becomes clear.

One wild guess might be to have a 30 amp circuit feeding a cluster of 5 lifts, with each lift fused (time delay) at 10 amps.
As for the size of the service feeding the shop, I'd be happy with the usual load calculation method, relying on the square footage allownace for 'general lighting.'

Re: load diversity factor for car parking lift [Re: renosteinke] #175270 02/26/08 01:54 AM
Joined: Jul 2002
Posts: 8,379
Trumpy Offline
Member
Hi there Theseus,
OK, you have 50 of these lifts, now, you have to figure in the fact that they will not all be running at the same time,or will they?, this is called a diversity factor.
For the purposes of supply, what voltage are you working with?
Unless you give more information on how your area of the world sizes electrical supply to buildings such as this, I'm sorry we can't help you.

Re: load diversity factor for car parking lift [Re: Trumpy] #175287 02/26/08 08:38 AM
Joined: Feb 2008
Posts: 12
T
theseus Offline OP
Member
Electrical data is as follows:
Main electrical supply 230/400V,50 Hz, 3 phase. Power consumption 3.0 kW. Fuse or automatic circuitbreaker 3 x16A slow blow.

Somebody suggested that the demand factor is 0.3,but I don't know why.Can I consider car parking lifts as elevators and use the 0.72 demand factor?

Re: load diversity factor for car parking lift [Re: theseus] #175288 02/26/08 08:46 AM
Joined: Feb 2008
Posts: 12
T
theseus Offline OP
Member
Thanks all.
These car parking lifts will be used in a parking lot.

Re: load diversity factor for car parking lift [Re: theseus] #175296 02/26/08 12:23 PM
Joined: Sep 2005
Posts: 153
W
Wolfgang Offline
Member
I suppose that those motors won't be charged completely but being overdimensioned will draw rather 4 or 5 than theoretical 6 Amps per phase.
Furthermore "downlifting" will draw less power than "uplifting".

Sounds like some 7 amps for both at a time?

So how many of those motors will run simultaneously? I'd take
50 - 100% security and check in a next step whether this power is easily available at your place. If not you rather should install a sort of "exclusion logic" than to invest in excessive copper graves.

Re: load diversity factor for car parking lift [Re: Wolfgang] #175348 02/27/08 10:54 AM
Joined: Feb 2008
Posts: 12
T
theseus Offline OP
Member
renosteinke Said:
One wild guess might be to have a 30 amp circuit feeding a cluster of 5 lifts, with each lift fused (time delay) at 10 amps.
As for the size of the service feeding the shop, I'd be happy with the usual load calculation method, relying on the square footage allownace for 'general lighting.'

Is that OK?
1) a 30 amp circuit feeding a cluster of 5 lifts, with each lift fused (time delay) at 10 amps.
2) the usual load calculation method, relying on the square footage allownace for 'general lighting.'

and what's the feeder breaker size?


Re: load diversity factor for car parking lift [Re: theseus] #175359 02/27/08 09:34 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
I did say "wild guess." laugh At the time, there was NO voltage info available ... any every area has its' own rules and practices.

When I said "30 amp circuit," I was thinking in terms of #10 wire and a 30 amp inverse time breaker. Our tap would allow you to feed the fused disconnects, because a) there are fuses in them and b) our smallest disconnects are rated for 30 amps (maximum load).
I took the liberty of assuming 208-230v single phase motors.

As far as the feeder breaker ... again, here we start off our load calculations with the square footage - not the appliances used. Since the loads are sporadic, I did not consider it necessary to place much weight on the appliance contribution to the lighting load.
A rough estimate of the space occupied, again a wild guess, my numbers suggest a 60 amp feed is plenty for the lifts, the lights, and the convenience outlets.

Re: load diversity factor for car parking lift [Re: renosteinke] #175364 02/28/08 08:33 AM
Joined: Feb 2008
Posts: 12
T
theseus Offline OP
Member
Hi,renosteinke.Thank you very much.
By the way,is there any reference books showing the load calculation of parking lot containing these parking lifts?


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,745 Are you busy
209,659 Re: Forum
197,004 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3