ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
A 5-20(20a) receptacle is legal on a 15a circuit?
by libellis - 10/10/21 12:46 PM
GFCI's pops in large numbers
by dsk - 10/07/21 03:46 PM
Backup Generator Done Right
by timmp - 10/06/21 02:07 PM
How's all our Non-US folks doing?
by dsk - 09/30/21 05:06 AM
Well I am back to stay (nearly 6 years)
by Bill Addiss - 09/26/21 11:09 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 5 guests, and 23 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#175136 02/23/08 10:16 AM
Joined: Nov 2004
Posts: 53
H
Member
Hello,

I have a rooftop vent fan (3HP 480V) that the customer wants to control with a frequency drive. The panel is within sight (in the shop below). Is a disco required on the roof and prior to the drive to provide lockout capability, or does one on the roof suffice?

Also, do you guys provide additional motor protection in addition to the drive? (assuming it provides overcurrent protection)

Thanks in advance,

2017 / 2014 NEC & Related Books and Study Guides
Joined: Apr 2003
Posts: 139
B
Member
I don't exactly follow your installation description. However, Part IX of Article 430 identifies all your requirements for providing disconnecting means.

You will need to determine where and how you are obtaining both overload and ground-fault / short-circuit protection of the motor. It is possible this is all being doen by the VFD.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Joined: Jul 2007
Posts: 1,335
S
Member
You still need a disconnect on the roof if the motor i accessible on the roof and you can use a VFD down in the control room. You also want to check that the rooftop unit will not be affected by the VFD control like built in alarm or control circuits since the VFD is altering the power.


"Live Awesome!" - Kevin Carosa
Joined: Mar 2003
Posts: 849
Y
Member
2005 N.E.C. 430.102 B States: Must be within sight of the MOTOR Unless meets Exceptions 430.102 (B) Exception (a)or(b).
Thats the way I read it anyway.

Joined: Jul 2007
Posts: 1,335
S
Member
If the motor can be serviced from the roof, the disconnect downstairs will not be in site.


"Live Awesome!" - Kevin Carosa
Joined: Mar 2003
Posts: 849
Y
Member
I agree that why I noted must be within sign . Kinda hard to see thru the roof!
BUT what if they had a skylight?
:))

Joined: Mar 2007
Posts: 101
M
Member
I also agree although it is in 440.14. Also was a service receptacle within 25 feet or on the roof with the equipment this is 210.63.

Joined: Jan 2005
Posts: 5,316
Cat Servant
Member
From a practical standpoint, such a motor need two different types of protection; overcurrent as well as overload.
Overcurrent protection is what you get from fuses and breakers. Overload protection is what you get from the heaters in the starter. It's quite possible for a VFD to provide this secondary protection.

As for the disconnect ... I wish folks would forget the fine print of the code, and look at the application from a servicing standpoint. Do you want to shut it off before you work on it - or not? If so, doesn't it make sense to have some disconnecting means at the site of the motor? Why make / expect the guy to run up and down ladders multiple times, hope his LOTO is adequate, worry about automatic controls, etc?

Joined: Sep 2002
Posts: 910
Likes: 1
N
Member
Originally Posted by renosteinke


As for the disconnect ... I wish folks would forget the fine print of the code, and look at the application from a servicing standpoint. Do you want to shut it off before you work on it - or not? If so, doesn't it make sense to have some disconnecting means at the site of the motor? Why make / expect the guy to run up and down ladders multiple times, hope his LOTO is adequate, worry about automatic controls, etc?


Thank you a little common sense is always in order.

Joined: Nov 2000
Posts: 2,148
R
Member
Mike,
Quote
I also agree although it is in 440.14.

Article 440 does not apply to vent fans.


Don(resqcapt19)
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
dsk 5
Popular Topics(Views)
284,541 Are you busy
217,274 Re: Forum
203,620 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5