arc -faults #175047
02/20/08 06:51 PM
02/20/08 06:51 PM
T
tomselectrc  Offline OP
Member
Joined: Mar 2004
Posts: 49
warren mi us
have a attic fan in bedroom, need arc-fault? tried a cutler hammer breaker keeps tripping. attic fan about 30 years old. any suggestions inspector wants arc fault

2017 / 2014 NEC & Related Books and Study Guides
Re: arc -faults [Re: tomselectrc] #175048
02/20/08 07:32 PM
02/20/08 07:32 PM
L
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
120V 15-20A, in a bedroom, Yes AFCI.
New fan.
Howed the inspector get involved? Remodel?

Re: arc -faults [Re: leland] #175049
02/20/08 07:41 PM
02/20/08 07:41 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Maybe it is time for a new fan. AFCI's include ground fault protection which trips at about 30ma. The fan that old could have defective insulation which would trip the AFCI. Another thing to investigate, if you haven't already, is the possibility of a grounded neutral conductor which will also cause a trip.


Few things are harder to put up with than the annoyance of a good example.
Re: arc -faults [Re: Tom] #175050
02/20/08 07:44 PM
02/20/08 07:44 PM
R
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
"attic fan" as in "in attic, mounted ON the roof" or one of them "whole house fans"??
I didnt think an attic fan needed AFCI

Re: arc -faults [Re: tomselectrc] #175052
02/20/08 09:39 PM
02/20/08 09:39 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Unless the fan is actually located IN the bedroom ... I don't see where the requirement for the AFCI exists. The code is pretty clear ... every "outlet" ... and a switch is not an outlet.

In a like manner, simply having the fan pull air from the bedroom does not place it 'in' the room. I suppose a bath fan, where the fan is directly mounted to a hole in the ceiling, could be considered 'in' the bedroom. Let there be even a foot of duct, though, and it's not in the bedroom.

Otherwise, I agree that the fan is likely in need of replacement.

Re: arc -faults [Re: renosteinke] #175053
02/20/08 10:04 PM
02/20/08 10:04 PM
S
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,334
Alaska
Put the fan on a different circuit that is not feeding the rooms


"Live Awesome!" - Kevin Carosa
Re: arc -faults [Re: sparkyinak] #175054
02/21/08 08:38 AM
02/21/08 08:38 AM
T
tomselectrc  Offline OP
Member
Joined: Mar 2004
Posts: 49
warren mi us
the fan is on it's own curcit,it is in the stairway that is in the bedroom. it is not in the attic.it is a 2 speed fan . check out all connection. next step is to see if breaker is bad.are there any exceptions to the arc-fault rule that i have missed?

Re: arc -faults [Re: tomselectrc] #175065
02/21/08 04:11 PM
02/21/08 04:11 PM
B
BPHgravity  Offline
Member
Joined: Apr 2003
Posts: 139
Port Charlotte, Florida
Exchanging the breaker to see if it is defective is a quick and easy way to eliminate that from the equation.

However, I agree with several of the above statements regarding the age of the equipment and it being the likely problem. 30 year old equipment will simply not be compatable with AFCI technology.

While it may not be practical or economically feasible to replace the entire fan assembly, you may be able to simply replace the motor and controller components.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Re: arc -faults [Re: BPHgravity] #175068
02/21/08 05:45 PM
02/21/08 05:45 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
Since this is an individual circuit it should be pretty easy to diagnose. At the panel (with the breaker off) check for continuity between the ground and neutral when disconnected from the bus. If it is anything but infinity that is probably the trouble (ground neutral short). Work your way back to the motor until you find it. Next step would be to temporarily hook it up to a regular breaker and hang your clamp on across the ground. It should stay zero. If you have something, I would suspect an intermittent grounded motor winding (real ground fault).


Greg Fretwell
Re: arc -faults [Re: gfretwell] #175092
02/22/08 09:37 AM
02/22/08 09:37 AM
T
tomselectrc  Offline OP
Member
Joined: Mar 2004
Posts: 49
warren mi us
thanks for the feedback i'm going to see if i can move the switch on the stairway landing hopefully he will except that instead of changeing the motor

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,168 Are you busy
185,639 Re: Forum
175,010 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.037s Queries: 16 (0.006s) Memory: 1.0258 MB (Peak: 1.2075 MB) Zlib enabled. Server Time: 2018-07-23 06:12:32 UTC