680.26 (C) Pool water......
States water must be bonded.. Now the pump I don't feel is in "Direct contact" with the water, Gaskets,seals,impeller etc.
So, now we do the 9 sq inch thing.
Does the light trim count? Wet niche of course would. My thought woud be to install a peice of stainless pipe in 1 of the lines. This seems to be an easy solution.
The season (here) is approaching, so thoughts would be great.
Lee
Last edited by leland; 02/14/08 08:16 AM.
|
|
|
|
Joined: Jul 2004
Posts: 10,007 Likes: 37
Member
|
A 2" metallic pipe nipple on the pump with a suitable clamp would meet the requirement, even with 1.5" pipe. (9.42 sq/in)
Most of the wet niches I see around here are PVC but there usually is a metal ring on the light. You would also be able to include a metal ladder or even the ladder cups if they are metal and under water.
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,412 Likes: 7
Member
|
Greg: Today's discussion regarding the ladder.... Pools here are closed for the winter, and the ladders are removed for the cover. Based on that, the water bond is not there with the ladder out. Comments??
John
|
|
|
|
Joined: Aug 2007
Posts: 853
OP
Member
|
YA, What Hotline1 said.
We don't all live in the sunshine state!! Haven't seen sun in 5 looong days!! Damn cold too!!
(all in jest- can't (don't know how) to find the icons)
Now the next step is to find (or make) an approved nipple with a lug on it.
|
|
|
|
Joined: Mar 2005
Posts: 1,213
Member
|
If steel rebar is considered a grounding electrode when of sufficient length in contact with concrete, wouldn't the pool water also be considered grounded by contact? Or does the liner completely negate that?
|
|
|
|
Joined: Jul 2004
Posts: 10,007 Likes: 37
Member
|
Steve, the issue they are talking about is a plastic pool, double insulated pump and all plastic nicheless light. If you have no other way to bond the water the 2008 requires some other piece of metal 9 sq/in to accomplish it. John If the ladder is out, the cups are still going to be there.
Greg Fretwell
|
|
|
|
Joined: Aug 2007
Posts: 853
OP
Member
|
John If the ladder is out, the cups are still going to be there. Greg, these cups are not typicaly in contact with the water are they? My pool has the drop in ladders, cups only in the deck, (In ground liner). No hand rail at the steps,though I suppose if there were one that would cover it. I think we will see a metalic coupleing,as discussed, arive shortly.This would be a nice convieniant and standard solution.
|
|
|
|
Joined: Jul 2004
Posts: 10,007 Likes: 37
Member
|
I am not really sure how many "plastic only" pools there are in the US. Concrete "in ground" is the norm here and the rebar makes this an excellent ground plane. The sun tears up plastic and I don't think I have ever seen the vinyl liner pools here except a few above ground. Usually they either go for a concrete pool or they abandon the pool idea altogether
Greg Fretwell
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
Greg, Up here I have seen in the last 9 years at least 7 plastic pools. I am not a big fan of these pools, but I have to inspect them. BTW, these pools are the only ones that I have seen problems with "Stray Voltage". The concrete or steel w/plastic liners never had any stray voltage ( to my knowledge) problems around here. John, If the the ladder is out for the winter, is the pool bonding that critical?  LOL, I mean is anyone going to swim up here in Jan? Today was a balmy 25-35 deg and sunny, a nice day for a walk, but not a swim.
|
|
|
|
Joined: Apr 2002
Posts: 7,412 Likes: 7
Member
|
Harold: My thoughts went down that road... Metal ladder connected mechanically to bonded cups. OK as a "water bond". I thought that would be an acceptable solution..... Comment was...'no good because ladder is removed when pool is covered' (winterized) My reply was...'who would/could be affected in any way by a covered/winterized pool?' Comment was to the effect that the install would not be code compliant.
Debate will continue at a future date.