If you are installing a GEC at a second building on a service do you still size to 250.66 on the service conductors or do you base it on the feeder?
Work Gear for Electricians and the Trades
Workgear for Electricians
The size of the feeder to the building in question.
Check out 250.32(E) 2005
OK I was just concerned about what a "supply conductor" really meant. I assumed it was the feeder but I wanted to hear it ... as a sanity check. Thanks
I agree it could be clearer.......