gfretwell
GEC size at second building?
-
01/23/08
08:17 PM
If you are installing a GEC at a second building on a service do you still size to 250.66 on the service conductors or do you base it on the feeder?
Posted By:
iwire
Re: GEC size at second building?
-
01/23/08
09:00 PM
The size of the feeder to the building in question.
Check out 250.32(E) 2005
Posted By:
gfretwell
Re: GEC size at second building?
-
01/24/08
04:39 AM
OK I was just concerned about what a "supply conductor" really meant. I assumed it was the feeder but I wanted to hear it ... as a sanity check. Thanks
Posted By:
iwire
Re: GEC size at second building?
-
01/24/08
09:44 AM
I agree it could be clearer.......
©