#173705 01/16/08 05:20 PM
Joined: Jan 2003
Posts: 21
R
rj Offline OP
Member
I am in need of some information about bolt in breakers compared to stabe ins. I know that you are suppost to have a better connection with a bolt in, but what about maintenace in the long run. Myself I would rahter work and maintain the stabe in. Any others with that feeling or that bolt in is the best way to go?
Thanks for any input on this.

rj #173706 01/16/08 05:27 PM
Joined: Jul 2007
Posts: 265
W
Member
I like the bolt in for areas with high load or vibration. I worked in manufacturing plants for about 16 years, most of the equipment was either Westinghouse or Square D bolt in type, all of it gave vary little trouble. As far as maint. goes we would shut down the panels once every other year and check the screws for tightness, I do not remember ever tightning one more than about 1/16 of a turn, of course all this was wired with copper wire, as it should be in an industrial setting.


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Aug 2007
Posts: 853
L
Member
Industrial: bolt in every time. reliability.

Resi: stab ins are fine, very low demand.

Joined: Mar 2005
Posts: 1,213
S
Member
Anywhere with potentially high fault current requires bolt-on, because the electromagnetic forces in a full-blown short-circuit fault can be enough to tear cables right out of set screws, and breakers right off the panel.

If you're just fed from a small transformer (ala residential size) or otherwise have low availible fault current, then it's less of an issue.

Joined: Dec 2000
Posts: 4,288
Member
I agree with the rest of the guys that in most cases I prefer a bolted connection.

That said:
The Square D "I-Line" breaker, their premium offering, is a plug in.

[Linked Image]



The lowly ITE-Bulldog Pushmatic is a bolt on breaker.

[Linked Image]

laugh



Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
Admin 3
dsk 2
Popular Topics(Views)
286,325 Are you busy
218,789 Re: Forum
204,945 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5