#173447 01/09/08 10:30 PM
Joined: Dec 2007
Posts: 35
H
Member
does anybody know where to find the answer to where do you reset a patient alarm in nurse call system at the nurses station or at the source?

Horizontal Ad
Joined: Mar 2004
Posts: 251
W
Member
Most are reset at the patient room.

Joined: May 2005
Posts: 984
Likes: 1
G
Member
They're generally acknowledged at the source to guarantee that someone actually walked into the room.


Ghost307
Joined: Jul 2005
Posts: 183
J
Member
A bit of both of the posts in my experience. They would get reset at the patient room, and can be acknowledged at a nurses station.

jay8 #173475 01/10/08 03:37 PM
Joined: Aug 2005
Posts: 265
S
Member
Same here - the ones we did were "silenced" at the nurse's station, but they had to physically go to the bed to reset the light.


Sixer

"Will it be cheaper if I drill the holes for you?"
Joined: May 2001
Posts: 378
F
Member
Call bells have a cancel button on the room panel and the desk.If the pendent is pulled from the wall or bad it will also call the desk and can't be canceled,replace it first.A system rest is usually done by shutting down and restarting the system.I try to cancel it at both ends replace the pendent and check the light bulbs above the door,then reset the system.If it's a maxi vox the in room board can blow a resister if an above door light is out and a call is triggered.It was a defective pin in the in room boards connector and Maxi vox knows about it.The ground MUST be checked and terminated as it will fry the board and or not work right on any system ive seen so far.
So the pendent and above door lights can trigger a constant call until replaced.
cheers

Last edited by frank; 01/10/08 07:11 PM.

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
337,508 Are you busy
262,894 Re: Forum
243,185 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5